Pump overload tripping at night

Users who are viewing this thread

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
The overload on my pump control box has tripped 3 out of the last 4 nights. It only happens at night and we wake up to no water. When I reset it, the pump runs fine all day and then it trips again over night. I have been trying to figure it out with no luck. I measured current in the 3 legs to the pump and got Red = 1.1A, Black = 10.7A and Yellow = 11.0A. I'm not that familiar with electrical issues so I'm not sure if this is normal. I have a 3/4 HP pump that I think is running on 240V. Any suggestions?
 
Last edited:

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
As a follow up, I measured the resistance between the legs on the motor at the well head. I got 9.2 Ohms Yellow-Red, 10.2 Ohms Red-Black and 2.8 Ohms Yellow to Black.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
In most homes the pump will have no reason to run during the overnight hours, so it does not sound like an overload trip.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
My water softener recharges at night. The overload on the control box is what is tripping. I've tried to reproduce it by forcing the pump to cycle repeatedly with no luck. Is there anything a softener can do to cause the overload to trip?
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
I've tried to reproduce it by forcing the pump to cycle repeatedly with no luck. Is there anything a softener can do to cause the overload to trip?
Is the softener on a completely different circuit? *Maybe* the softener is somehow reducing voltage to the pump and the pump's amperage is going too high. Try manually cycling the softener while you watch.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
The softener plugs into the GFCI outlet in the garage so I don't think it's on the same circuit. Electrical is not my specialty. I'll dig into that a little more when I get home. I did manual cycle the softener and it did not trip.
 

Texas Wellman

In the Trades
Messages
1,035
Reaction score
59
Points
48
Location
SE Texas-Coastal
Wow. Your first post gave all the info I needed to determine the problem. Your pump is pulling way too many amps.

That motor, according to the charts, should pull no more than 8 amps. Your pump/motor is fixing to quit, you better get it fixed ASAP.
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
TW is right, a 3/4 HP should pull no more than 8 amps. The real question is, how is it working at all? Probably already survived the average of 7 years and cycled itself to death.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
The pump has been in operation for 3 yrs as of October 16th when we moved into the newly built house. I was assuming it was the pump.
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
The average life of a submersible is 7 years. If it only lasted 3 years, it must be cycing a lot. One of your neighbors pumps doesn't cycle much and will last 11 years. That is why the average is 7 years.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
The softener plugs into the GFCI outlet in the garage so I don't think it's on the same circuit.
The pump gets 120V from one line and then 120V from the other to get a total of 240V, and the softener gets 120V from one of those lines at the breaker panel. However, I have seen situations where a 120V outlet has been illegally tapped from one of those lines (such as at or near the pump) ... but that is obviously not your case there in a relatively new home.
 

LLigetfa

DIYer, not in the trades
Messages
7,502
Reaction score
577
Points
113
Location
NW Ontario, Canada
I had a neighbor (who happens to be an electrician) mis-diagnose his pump by measuring amps. Turned out to just be a bad heatshrink that was sending current to ground. (Yes JW, current can go to ground)

The jury is still out until the pump is pulled and the wire inspected.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
The pump gets 120V from one line and then 120V from the other to get a total of 240V, and the softener gets 120V from one of those lines at the breaker panel. However, I have seen situations where a 120V outlet has been illegally tapped from one of those lines (such as at or near the pump) ... but that is obviously not your case there in a relatively new home.

Don't make any assumptions here. I actually had to sue the builder of my home for poor construction. I can't even figure out who dug the well because he fled to the Virgin Islands during the court case. Long story...
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I doubt that yours is hooked up to the wrong voltage. But any driller who flees to the islands or even spends the off season there is probably not reputable.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
I looked up the AIM manual but I don't know if it applies to my pump yet. Due to the previously mentioned lawsuit with my builder, all of the information about my house, including the well, is at the county courthouse. At this point, I don't know for sure that I have 3/4 HP pump or who the manufacturer is. I am going to the courthouse today to see what kind of pump I have and then try to figure out which way to go from there. I talked to a well guy in Weatherford today about replacing the pump and he said he thinks the current sounds right so I'm even more confused. But I didn't ignore your advice. I just want to be completely sure before I start pulling the pump out of the ground.
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I should have caught that. There is no reset button in a 3/4 control box. It would have to be a 1.5 HP or bigger. And those ohm and amp numbers are good for a 1.5 HP. So maybe you just have a bad start cap and something is leaking off during the night.
 

Ehuddle

New Member
Messages
16
Reaction score
0
Points
0
Location
weatherford, tx
I should have caught that. There is no reset button in a 3/4 control box. It would have to be a 1.5 HP or bigger. And those ohm and amp numbers are good for a 1.5 HP. So maybe you just have a bad start cap and something is leaking off during the night.

It is a 1.5 HP control box. Centripro CB15412CR. Please excuse my ignorance but does this mean it has to be a 1.5 HP pump? I didn't find any info on the pump at the courthouse so now I have to tear my house apart or call every well service around to see if I can find who dug the well.
 

Texas Wellman

In the Trades
Messages
1,035
Reaction score
59
Points
48
Location
SE Texas-Coastal
I thought about the control box/HP mismatch too in your original post.

What made you think it's a 3/4 HP? Those numbers are OK for a 1.5 HP, as valveman said.

Might just try changing the box and keeping an eye on it.
 