I've got a 3 year old Reliance GSW rental tank - gas - power vent - 6G40NVH-FV-02 - B4743 that has started making thumping noises. Best as I can tell, the water is on the verge of boiling... vapour bubbles form and then quickly condense. It didn't always do this and it's getting annoying. It started after the gas valve was replaced but don't know if it's related. Just one more noise in a long list of noises. Water temp is the same as always.
 

BizzyBeePlumbing

New Member
Messages
23
Reaction score
0
Points
0
Location
Raleigh,Nc
I would pull the drain valve, install a 3/4" nipple and a ball valve and flush the unit. Jim is probably right, sediment in the bottom of the tank
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Could be mineral deposits...
Ja, that crossed my mind. I'm thinking that they are probably like potato chips though that flaked off and would not flush out the drain even if I changed it out to a full port ball valve. Probably not as bad as the following classic pic. I've opened the cheap plastic drain and only clear water comes out.

I found this how-to that calls for a tube to be inserted like liposuction.
http://waterheatertimer.org/Clean-sediment-out-of-water-heater.html


189451_115133385228509_100265773381937_118795_6390953_n.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If water can't flow (convection) over an area that is being heated because a little is trapped behind a mineral deposit, eventually it will flash into steam, break through that little mineral bubble, and make noises. The more mineral deposits, the more this happens. That mini steam explosion takes its toll eventually, but is mostly annoying.
 
Messages
951
Reaction score
6
Points
18
Location
Midwest
I've got a 3 year old Reliance GSW rental tank - gas - power vent - 6G40NVH-FV-02 - B4743 that has started making thumping noises. Best as I can tell, the water is on the verge of boiling... vapour bubbles form and then quickly condense. It didn't always do this and it's getting annoying. It started after the gas valve was replaced but don't know if it's related. Just one more noise in a long list of noises. Water temp is the same as always.

How hard is the water?

What is the temp set point?

I'll take your word for it that this is incipient (or full fledged) boiling with normal conditions. We had extremely hard water when I was a kid and as the oldest I used a long handled spoon to scrape out a lot of insoluble carbonate (retrograde solubility of various compounds) both at home and at the water heater in the dairy barn. Although I did a couple of electric element replacements the tanks were still running when I graduated from college and went my own way.

Retrograde solubility is a bitch. Magnesium and calcium carbonates actually precipitate as temp increases--the opposite of normal behaviour where most materials become more soluble with temp. If you have soft water , (as I had on moving to Texas) you will be asking: "What the hell is he talking about???"
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
I don't recall the numbers but I have hard water. The old State tank sprung a leak after 10 years and it was very slow to drain so I'm guessing it was pretty crudded up. I tried to trip the TPR at the time thinking I'd break the vacuum to drain faster but it turned out to be all crudded up and wouldn't move.

Not sure about the temp set point but it is higher than the default. A 50/50 mix of hot and cold is about right for filling the wife's soaker tub.

I did the math and figured I'd break even renting versus buying if it only lasts 10 years. The only thing I didn't think through is if it lasts much longer and fills up with scale like the pic above and the rental company doesn't want to replace it. Then I'd have to cancel and buy a new tank or go tankless.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If a tank gets that full of deposits, it wouldn't provide much hot water and that alone, rather than a leak, should consitute a valid reason to replace it. You'd have to read the fine print carefully, though.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Bumping an old thread. So I built this house in '98 and '99. My first State brand HWT lasted only 10 years.

I did the math and figured I'd break even renting versus buying if it only lasts 10 years.
What I didn't factor in my math was the additional cost of service calls and replacement parts. The GSW that replaced the State had 3 service calls in it's short life which ended yesterday. Since it was a rental, the service calls didn't cost me a dime. Now that the GSW failed, they replaced it with a Rheem at no cost to me.

My original State HWT was a passive vent with a 6 inch direct vent pipe. The GSW was a little taller but they could run the 2 inch PVC vent out through the original 6 inch chase which they made up flashings for. The Rheem however is taller and they had to drill a new 2 inch hole above the original 6 inch hole that I then had to plug up. I was lucky that the 6 inch hole was entirely in one strip of siding and didn't span two strips and that it was a short section between my hydro meter and a window. Fortunately I kept a small piece of the vinyl siding so I could pull off the section, remove the part with the 6 inch hole, and stagger the seams so that it doesn't look like a patch job.

As for the installer, I was not impressed. I had a CO detector plugged into a wall outlet next to the powervent right above the HWT. He didn't remove it and so when he was sweating some fittings, melted the plastic case on the detector. When I looked in on his progress the detector was removed, so he must have realized what he did and removed it and then put it back when he was done without telling me he melted it.

When he drilled the 2 inch hole, rather than risk breaking the vinyl siding, he marked it with a fat-tip Sharpie and cut it inside the line with snips. I would have used a smaller circle template so as to cut away the black Sharpie line. Also would have used the hole saw in reverse so as not to shatter the vinyl. He not only left the thick black line but he also made the hole too big. Then he wanted to use clear silicone seal to fill the gap. I have white siding! Now I have to get some white silicone seal to fill the huge gap and lather it on thick enough to cover the black Sharpie line.
 