Splicing a Ground Wire

Users who are viewing this thread

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
Hello,

A ground wire was torn during excavation. Can this be spliced or does a new wire have to be run?

Thanks,
Bill
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
Need some more information to give anything other than a general answer, but any wire that is broken is allowed to be repaired. How it is repaired depends on what kind of ground wire it is.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
By "ground wire" do you mean a "wire in the ground" or a "grounding" wire? There are few "single" ground wires which could, or would, be where an excavator could damage them, unless it was doing something like interconnecting power line towers, or poles.
 

Cwhyu2

Consultant
Messages
1,615
Reaction score
22
Points
38
Location
Cincinnati OH
By "ground wire" do you mean a "wire in the ground" or a "grounding" wire? There are few "single" ground wires which could, or would, be where an excavator could damage them, unless it was doing something like interconnecting power line towers, or poles.
That is what I have been wondering about.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
It's a grounding wire (bare copper) that is run into the ground attached to grounding rods. It was torn by the excavator.

Thanks,
Bill
 

Jim Port

Electrical Contractor
Messages
156
Reaction score
0
Points
0
Location
Maryland
Website
www.manta.com
The conductor can be repaired, but, it must be repaired with an exothermic connection like a Cadweld or an irreversible crimp. It might be easier to just replace it from the panel to the first rod.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The ground wire should be so close to the building that he should have damaged the house at the same time. But, it should also be such a short route that replacing it would be easier than going to the trouble of locating a crimping tool and the splices.
 