moving an island

Users who are viewing this thread

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
Noo not an earthquake, just a kitchen remodel :D

Re-doing our kitchen that is original to our 1980 slab-on-grade Florida home. Part of the project is to turn a built-in table into a counter-height island with seating. To that end, the whole island is moving closer to the kitchen work area. Electrical conduit is running from a near wall to the current island under an inch or two of slab. Some of the tile is coming up anyway so I will be able to dig the conduit up, but it must be redirected. It's currently bent away from the kitchen and I need it in the opposite direction.

SO, my questions are:

Is what is in my slab likely the same "EMT" that I can get from a box store today? I have done electrical boxes with conduit in my garage, this stuff is much thinner.

What is the correct way to change the direction of the conduit? Cut and attach an elbow? How are fittings attached for in-slab work?

Wrong section I know but while I'm at it, any harm in tiling under the new island? I have read a lot on this and it seems personal preference? Seems like less work for me w/no island in the way.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Don't know on the electrical, but it's easier (but more materials, and therefore could be more expensive especially if the tile are pricey) to tile under the island, then install. This gives you the advantage of not having to try to cut all those extra tiles, caulking and grouting under the toekick, and, if you decide to take it out, it will probably make installation of a new island cabinet easier as the size then isn't critical. It does make it harder to anchor the island, but in concrete, probably not by much. You'll probably need a diamond core bit to drill a hole in the tile, although some softer tile can be drilled with carbide.
 

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
Thanks Jadnashua, we're only talking about 75 sq ft of tile so I think I'll save myself some trouble and tile before setting the cabinet. I plan to tapcon in some 2x4's and screw the cabinet to that, so will be same with/without tile.

As for the electrical, still want to hear from the experts but I'm thinking I just need a 90 degree bend and some compression fittings. I will be doing this under owner/builder permit so want to make sure it's correct though.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
No EMT as it will not last very long. It needs to be PVC and you will need to cut out the concrete to access the new location. Use a factory 90 but do not use an elbow as you will not have access to it after pouring the concrete you will need to cut out in order to access the original conduit
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
What is the correct way to change the direction of the conduit? Cut and attach an elbow? How are fittings attached for in-slab work?
Yes cut back and add some more conduit if needed, then add an elbow.
The conduit and fittings in the slab should be PVC and are glued together with PVC cement.
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
No EMT as it will not last very long. It needs to be PVC and you will need to cut out the concrete to access the new location. Use a factory 90 but do not use an elbow as you will not have access to it after pouring the concrete you will need to cut out in order to access the original conduit

Why does he need access to the ninety?
 

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
I'd rather not replace the whole thing with PVC, that would require pulling up tiles I didn't intend to and digging into a wall I plan to leave alone. Maybe it's not EMT? I'll try to get a picture tonight. As I said this house was built in 1980 (31 years old) so the conduit has lasted at least that long. Would it be illegal/immoral/fattening to join the existing conduit to PVC?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
If this conduit has been installed for 30+ years when you open the concrete to expose the conduit you can see for yourself what will happen to EMT when used as you suggest if EMT was used.
I would bet that there is not enough wall left to install a fitting to so if it is EMT you might not have a choice but to replace the entire run.
 

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
Ok maybe it's not EMT. What would have been normally installed in a slab-on-grade home 30 years ago?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Good question and one that you will have to answer. You should be able to see what type of installation that was made where it enters the bottom of the cabinet now.

If I had been the one making the installation it would have been PVC with THHN/THWN copper #12 conductors consisting of one black one white and one green or it would have been UF cable with a short sleeve of PVC where it went through the concrete and buried in the dirt below the concrete.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
EMT. galvanized, in a dry slab should outlast the cement. Lets seee.... how about all that raw rebar in a road, or galvanized or epoxy coated rebar in a bridge? Leave it alone.

Would be good to change the wires though.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
The key to your statement is dry

Under a slab in contact with earth is far from dry.

I have removed many EMT pipes from a poured slab and found nothing but wires and rust.
 

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
Ok gents made some progress over the weekend. I removed the island and dug out the conduit, it was a little rusted but only in the section I cut off so no reason to replace all of it. I installed a new section with compression fittings in another trench I dug. How did I do?

20110626003.jpg
20110626004.jpg


I also learned how NOT to bend EMT.

20110626005.jpg
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
If you needed the dust storm and the excercise, it was a great validation of my point that emt in dry cement lasts as long as the cement.
 
Last edited:

Mr. Fixit

New Member
Messages
8
Reaction score
0
Points
0
Location
Florida
It was both of those but also necessary as the island that this circuit services is moving. Was just looking for some final verification that it looks done correctly before I seal it up.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Told you before that while previously they allowed emt, if you want validation for today's codes, you won't get it. Work done today is supposed to meet today's codes. Yes, it will probably last a long time, but if you had a bit more moisture under/in the slab, you'd have a pile of rust. The codes are written for those what-if situations so things will work anywhere/anytime and last. You are not allowed to decide on your own what good enough is when you wish to get it inspected.
 