I opted to install a switched outlet under the sink for the disposal (rather than a hard wire with a whip). Should I install a GFCI?

Also, there will be a non-switched outlet for a potential hot water dispenser. I thought I remembered seeing in one set of specs that they recommend a GFCI but the specs I printed for a model we are considering do not say anything about recommending GFCI.

My inclination is always GFCI near water. But will there be tripping issues with a switched appliance such as a G/D?
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
...will there be tripping issues with a switched appliance such as a G/D?
Sorry, I cannot answer your first question but as for this one, I think it could have a propensity to trip. All my outdoor recptacles are GFCI and when I use them to power motorized tools like saws and drills, they easily trip when shutting off the tool. I think it has to do with the collapsing magnetic field on the motor coils and/or the motor becoming a generator. Possibly not all GFCIs are created equal and YMMV.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I opted to install a switched outlet under the sink for the disposal (rather than a hard wire with a whip). Should I install a GFCI?

Also, there will be a non-switched outlet for a potential hot water dispenser. I thought I remembered seeing in one set of specs that they recommend a GFCI but the specs I printed for a model we are considering do not say anything about recommending GFCI.

My inclination is always GFCI near water. But will there be tripping issues with a switched appliance such as a G/D?

Is this a kitchen sink? If so then no GFCI required
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
If it is a regular wall switch then it should be GFCI protected. Don't most disposers have an air coupled push button?
41mXPhrL6UL.jpg
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
I agree with jwelectric. I've never seen a GFI on a disposer.

And I sold very few air switches for disposers. They are handy if there is no space on the wall for a switch though.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Would you like to provide a code citation for this?
Not really. The operative question was "should", not "must" as was my advice. There is no point in me quoting Canadian Electrical Code to the OP who lives in NY.

If you can ground one hand on the sink or tap and reach the unprotected switch with the other perhaps wet hand, common sense dictates that a GFCI "should" be used. Canadian code may dictate it too. When I built my home 12 years ago, I did my own wiring and read through the code books at the time, but am too lazy to scour through it now.

A quick google search suggests that GFCI outlets must be installed on all receptacles within 1.5 meters of a sink.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Here is an excerpt from my google search.

GFCI Protection of Kitchen Counter Receptacles
Rule 26-700(12)
The 2002 edition of the Ontario Electrical Safety Code includes an Ontario amendment to Rule 26-700, which requires Ground Fault Circuit Interrupter (GFCI) protection for Kitchen Counter receptacles effective January 1, 2003. The new Subrule (26-700(12) states that effective January 2003:
(12) Receptacles located in kitchens and installed within 1 m of a kitchen sink along the wall behind counter work surfaces shall be protected by a ground fault circuit interrupter of the Class A type.
Appendix B note: Distance of 1 m is measured from edge of kitchen sink.
The following guidelines shall be used for consistent interpretation and application of this new subrule effective January 1, 2003.
1. This rule applies to all receptacle installations located within 1 m of a kitchen sink along the wall behind counter work surfaces where the plans or application for inspection is received on or after January 1, 2003.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
So........are you planning on using the disposer like a toaster? And have it on the counter?

Everybody knows that the outlets "above" the counter are GFI''d
That wasn't' the question though. The question was for a disposer that is "below" the counter.
Below; opposite of above.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
I realize the outlet is "Under" the counter but the switch presumably will be "Above" the counter. I'm sure I can find some code reference to a light/fan/switch near a sink or bathtub/shower etc. We GFCI protect anything that is within easy reach of a sink/tub/shower/etc. Why would a disposer be any different?


We see here in a lot of new construction that the light switch is on the outside of the bathroom. Mine is on the inside, albeit protected by GFCI. The same with my laundry room. Now, I stopped short of using GFCI on the washer because it would likely trip it. I don't generally operate the wash machine while I have a hand in the sink or on the tap. A garbage disposer however is more prone to be operated whilst touching the faucet which is why they came out with those air switches. If you guys want to build to minimum code, that's your choice.

I would choose not to use a GFCI but then I would use an air switch.​
 
Last edited by a moderator:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Being that Canada uses the NEC there is no requirement to GFCI a receptacle below the sink there just as there is no requirement to protect the receptacle with GFCI here.

Switches are not required to be GFCI protected at all in any location.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
A typical light switch would have to be in really bad shape to get a shock off of it. Now, a static discharge if you happen to hit an exposed cover screw could happen!
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I'm sure I can find some code reference to a light/fan/switch near a sink or bathtub/shower etc. We GFCI protect anything that is within easy reach of a sink/tub/shower/etc. Why would a disposer be any different?
No, this is a case of not knowing the code and throwing an OVER coded situation at it to cover yourself, in the guise of "safety".

So you wired you own house a few years ago, and "read through the code books at the time", and you think this give you the authority/experience to be giving advice on electrical mesage boards???
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
So we have a guy that works in an IT department for his day job that used an air switch in his home.

And all the electrical contractors that wire homes for a living, that know what the code says and can wire to code saying; No. a GFI is not used.
Sounds like the question has been answered.

NO GFI needed for a disposer.
Thanks to all the sparky's that had a handle on this.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
...and you think this give you the authority/experience to be giving advice on electrical mesage boards???
No, I was not claiming expertise and you quoted me out of context. What I said was "read through the code books at the time, but am too lazy to scour through it now" with the emphasis on lazy. I don't know why eveyone is twisting this into a "CODE" issue. I never claimed to know, nor did I quote NY code and only gave a code example to show how far Ontario code goes in this regard. If you feel minimum code is fine that's your (professional) opinion. It would appear Ontario electrical safety inspectors may have a differing professional opinion. If I were to err, I would prefer to err on the side of caution, spending a few extra dollars for an air switch or GFCI. Again, my operative word was "should" and that is my personal (not professional) opinion.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
No, I was not claiming expertise and you quoted me out of context.
I realize that you were not, and NO I did not. Yet you really do not know the codes and even common practices but you are giving advice here on electrical matters.


I don't know why eveyone is twisting this into a "CODE" issue.
"Twisting"??? You CANNOT be serious. :rolleyes:
It IS a code issue!


If you feel minimum code is fine that's your (professional) opinion.
Yes, I certainly do feel code minimums are absolutely safe. Without question.
That said, rarely do most professionals wire to absolute code minimum.


This is NOT a NY thing. Bottom line, in the US disposals are typically NOT wire through a GFI. Simple as that.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Sorry, I cannot answer your first question but as for this one, I think it could have a propensity to trip. All my outdoor recptacles are GFCI and when I use them to power motorized tools like saws and drills, they easily trip when shutting off the tool. I think it has to do with the collapsing magnetic field on the motor coils and/or the motor becoming a generator. Possibly not all GFCIs are created equal and YMMV.
Should you have some tool that is tripping your outside receptacles then your tool needs attention or replacement. The GFCI device is doing what it was designed to do.
What is a YMMV?
If it is a regular wall switch then it should be GFCI protected. Don't most disposers have an air coupled push button?
I do believe you have crossed over the boundary of knowing and guessing or inserting opinion in a matter in which you have little or no knowledge. Neither the US or Canadian codes require a switch to be ground fault protected,

Not really. The operative question was "should", not "must" as was my advice. There is no point in me quoting Canadian Electrical Code to the OP who lives in NY.
This makes me wonder just what your point is in this post. Why do you think the switch should be GFCI Protected? In your next statement you say that the Canadian code requires it to be protected but refuse to post a quote from the code.

If you can ground one hand on the sink or tap and reach the unprotected switch with the other perhaps wet hand, common sense dictates that a GFCI "should" be used. Canadian code may dictate it too. When I built my home 12 years ago, I did my own wiring and read through the code books at the time, but am too lazy to scour through it now.
If the sink is not in contact with earth is some matter how is it grounded? I think you are grasping at straws here as you sure don’t understand the concepts of grounding and bonding.

1.
Here is an excerpt from my google search. GFCI Protection of Kitchen Counter Receptacles
Rule 26-700(12)
The 2002 edition of the Ontario Electrical Safety Code includes an Ontario amendment to Rule 26-700, which requires Ground Fault Circuit Interrupter (GFCI) protection for Kitchen Counter receptacles effective January 1, 2003. The new Subrule (26-700(12) states that effective January 2003:
(12) Receptacles located in kitchens and installed within 1 m of a kitchen sink along the wall behind counter work surfaces shall be protected by a ground fault circuit interrupter of the Class A type.
Appendix B note: Distance of 1 m is measured from edge of kitchen sink.
The following guidelines shall be used for consistent interpretation and application of this new subrule effective January 1, 2003.
1. This rule applies to all receptacle installations located within 1 m of a kitchen sink along the wall behind counter work surfaces where the plans or application for inspection is received on or after January 1, 2003.
Dang if I can find one word from this quote that says a “switch” is required to be GFCI protected. Shucks I only see the requirement for countertop receptacles which wouldn’t include one under the cabinet.


I realize the outlet is "Under" the counter but the switch presumably will be "Above" the counter. I'm sure I can find some code reference to a light/fan/switch near a sink or bathtub/shower etc. We GFCI protect anything that is within easy reach of a sink/tub/shower/etc. Why would a disposer be any different?
But your code section says nothing about a switch. The switch is something you have come up with. The receptacle for the disposer is under the sink not above the sink.


We see here in a lot of new construction that the light switch is on the outside of the bathroom. Mine is on the inside, albeit protected by GFCI. The same with my laundry room. Now, I stopped short of using GFCI on the washer because it would likely trip it. I don't generally operate the wash machine while I have a hand in the sink or on the tap. A garbage disposer however is more prone to be operated whilst touching the faucet which is why they came out with those air switches. If you guys want to build to minimum code, that's your choice.

I would choose not to use a GFCI but then I would use an air switch.​
I say that if this is true then those living north of the boarder have completely lost what few brains they had left. As to the washing machine if the receptacle is located within 6 feet of a sink then the washing machine receptacle would be required to be GFCI protected. Should the washing machine trip the GFCI the there is something wrong with the washing machine.
All this bull waste of collapsing magnetic fields tripping a GFCI device is some idiots way of trying to explain something they know nothing about. It simply doesn’t happen.
 