loud howling noise coming from pressure regulator

Users who are viewing this thread

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
Hello i have a question. i had a very loud noise in my basement at my pressure regulator, i can hear the noise when the shower is on or when the washing machine is on or any faucet. so I had a plumber come out and replace the pressure regulator , he then hooked up a gauge and the gauge read 50 psi. after about 2 days later i again heard the loud noise, so i turned on the shower and went downstairs and when i put my hand on the pressure regulator the noise quite, is there a way to correct this. im pretty handy , the pressure regulator is soldered in and my water lines are 3/4" copper , they are all strapped down but the regulator is not strapped it is soldered onto the pipes im not sure if that is the problem, Now im thinking my old pressure regulator was not bad, because this new one has been installed and im having the same problems, any advice would be greatly appreciated my wife is driving me crazy, she wants this howling noise to stop. thanks.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Do you have an expansion tank? Has the tank failed (i.e., is it full of water - it should be mostly empty and full of air)? Buy yourself a gauge for about $10 and check it yourself. What is the pressure on the inlet side? Watch the pressure on the output side, especially after tanking a shower or using a bunch of hot water which will cause the WH to turn on. Hot water expands, and if there's no expansion tank, or yours has failed, it raises the pressure until the weakest thing leaks to relieve it, or if not high enough, just results in it being (momentarily until you use some water) high.

Make sure that your main water valve is fully open. and the one(s) at the WH.
 

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
hello jadnashua thanks for the reply. i do not have an expansion tank on my water heater. the incoming water pressure after the regulator is 50 psi. i have a full port 3/4" shut off valve for my main water supply it is fully opened. i have never had an expansion tank on any of the water heaters at this house. should i install an expansion tank on my water heater to resolve the loud howling noise coming from the pressure regulator. its really weird that when i grab the pressure regulator and hold onto it the noise completely stops......... to be honest im not sure when my wife first started hearing this loud noise, she said she was washing clothes one day and all of a sudden she heard the loud noise. so thats when i had the pressure regulator replaced and at the same time i had the water heater replaced because the old water heater was 11 years old and i normally replace them at that mark if they last that long. the new water heater and the new regulator are now 2 months old. the estate we live at has about 70 homes and there are only 2 residence that have the expansion tank on there water heater , my neighbors live 6 feet away and they have no noise coming from there pressure regulator and they have no expansion tank. i will install one if you think that will resolve the issue , thanks again for the reply....
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
I don't see the expansion tank doing anything for the noise. However it may be needed for thermal expansion. That would depend on whether or not your PRV has an internal bypass and the supplied pressure from the street.

I'm curious though about what your supplied pressure is...
Do you know?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
A PRV acts like a variable check valve...water goes one way, but not the other. So, when the volume of the water in the house expands from heating cold water in the tank, the pressure will rise without someplace for it to go - the PRV can't work backwards. Without a PRV, it pushes back to the street. Some cities are now putting checkvalves in/near the meter to prevent that as it is safer - if your water for some reason got polluted, you couldn't push it back into the supply to pollute others (like if you left a hose in a puddle and there was a hiccup in the pressure). So, with a closed system, you need some place for the water to expand, thus the expansion tank.

A PRV can be made with a bypass valve in it to help with that situation. But, if the external pressure is quite high, you'll still get an overpressure situation in the house, so it's not a good idea to rely on it. If you were getting high pressure in the house because of expansion, and the PRV wasn't operating properly, it might make some noise as the internal pressure rose.

ANY closed system with a heater needs an expansion tank.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
when i put my hand on the pressure regulator the noise quite, is there a way to correct this. im pretty handy
Your hand pressure damps out, or deforms things enough to prevent, the oscillation.

Usually I recommend finding the root cause but in this case I'd say temporarily duplicate your hand pressure with some kind of homemade fixture anchored to the wall or to pipes or to the regulator itself.
Maybe just putting mild pressure on the nearby pipes also stops it.

There's a small chance that this fix will work for a few days and the noise will return even with the fix in place. In any case you may get some clues as to the cause.

But, being that new it could also be "infant mortality"
http://en.wikipedia.org/wiki/Bathtub_curve
these failures are due to factory defects.
 
Last edited:

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
hello hj. this is the second pressure regulator i had installed because i thought the last one was bad because of the loud noise, would two different plumbers have installed the regulator backwards twice.........
 

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
A PRV acts like a variable check valve...water goes one way, but not the other. So, when the volume of the water in the house expands from heating cold water in the tank, the pressure will rise without someplace for it to go - the PRV can't work backwards. Without a PRV, it pushes back to the street. Some cities are now putting checkvalves in/near the meter to prevent that as it is safer - if your water for some reason got polluted, you couldn't push it back into the supply to pollute others (like if you left a hose in a puddle and there was a hiccup in the pressure). So, with a closed system, you need some place for the water to expand, thus the expansion tank.

A PRV can be made with a bypass valve in it to help with that situation. But, if the external pressure is quite high, you'll still get an overpressure situation in the house, so it's not a good idea to rely on it. If you were getting high pressure in the house because of expansion, and the PRV wasn't operating properly, it might make some noise as the internal pressure rose.

ANY closed system with a heater needs an expansion tank.

So i should install the expansion tank anyways for safety. Thanks.
 
Last edited:

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
Your hand pressure damps out, or deforms things enough to prevent, the oscillation.

Usually I recommend finding the root cause but in this case I'd say temporarily duplicate your hand pressure with some kind of homemade fixture anchored to the wall or to pipes or to the regulator itself.
Maybe just putting mild pressure on the nearby pipes also stops it.

There's a small chance that this fix will work for a few days and the noise will return even with the fix in place. In any case you may get some clues as to the cause.

But, being that new it could also be "infant mortality"
http://en.wikipedia.org/wiki/Bathtub_curve
these failures are due to factory defects.


Hello thatguy . i will try what you said to do. but what would you think the root cause is.. i have 96 psi water pressure coming in from city. i have 3/4" copper pipe throughout my entire house. the pressure regulator is brand new the water pressure after the regulator is 50 psi, my water heater is also brand new (bradford white). the pressure regulator is not strapped down to anything. the plumber soldered it onto the copper pipe, the copper pipe is mounted to cieling in basement. could vibration be causing it to make the howling noise. if i do strap it somehow what type of straps do you recommend..... Thanks.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
There is an arrow on the outside of the PRV, check to see that it is point TOWARDS the house side. I have not seen any PRV make noises unless one of those two conditions existed.
 

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
hello hj, i turned off the 3/4" shut off ball valve in my house and then i took channel locks and un-screwed the union side of the pressure regulator and then i turned the 3/4" shut off valve back on a little bit and water came flying out of the un-screwed side of the regulator there is an arrow as you said and it is pointing away from the 3/4" shut off valve towards the house in the direction of the water flow ............
 
Last edited:

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
There is an arrow on the outside of the PRV, check to see that it is point TOWARDS the house side. I have not seen any PRV make noises unless one of those two conditions existed.

Should i go and buy another pressure regulator and install it....... the regulator the plumber put on says watts on it..... and its all brass.. one side has a soldered male threaded adapter and the other side has a soldered union. but i guess i could have gotten two bad regulators beings i have the worst luck in the world....
 

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
Or else something is making two perfectly good regulators fail.

Can you post the noise on YouTube?

I can try and record the sound. The sound is like a loud whistle noise. if there is no faucets on , there is no sound. but when a faucet is turned on it sounds like a whisling noise at prv and if i put my hand on the prv the sound is gone...........
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Interesting that putting your hand on it silences the noise.

Try putting a couple of hangers on each side of it....
 

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
Interesting that putting your hand on it silences the noise.

Try putting a couple of hangers on each side of it....

thanks redwood....................... i put a hanger on each side and the noise is gone......... i am so glad , because my wife was driving me crazy.. Thanks for the help. this site really helped out thanks to all the pros........ THANKS AGAIN.....................
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Now that you have eliminated the "symptoms" what are you going to do about the problem that caused them in the first place, because PRVs do NOT whistle even if they are unsupported? It could be that the noise is actually occurring somewhere else, such as a water softener, but the PRV was just a point of resonance.
 
Last edited:

rayjoe123

New Member
Messages
18
Reaction score
0
Points
0
Location
pittsburgh, pa
Website
en.wikipedia.org
Now that you have eliminated the "symptoms" what are you going to do about the problem that caused them in the first place, because PRVs do NOT whistle even if they are unsupported? It could be that the noise is actually occurring somewhere else, such as a water softener, but the PRV was just a point of resonance.

i might have to call in a plumber again. to find out why it was whistling. i have no water softners in the house. the first prv that i replaced was about 11 years old . and when we heard the whisling we just thought the valve was bad so we called in a plumber and he checked the water after the prv and it read 93 psi , he said it should only read 50 psi , so he replaced it, and then a couple days later we heard the noise again. so we called in another plumber and he checked the new prv and said it read 50 psi , but he replaced it anyways to make sure that there was no internal part that came loose. and then after that the prv he put on still made the noise, lol. so one day i put my hand on it and the noise stopped. i did not know what to do so i got on here for help. and once i put the hangers on like redwood suggested the noise stopped, and the psi after the prv is 50 psi.. im still not to sure why the noise stopped after i installed the hangers i was thinking that maybe it needed to be more secured to the wall. i hate to call another plumber in and him charge me and not fix the problem like the two before him did..... right now i have $600 dollars into this prv problem........ what do u suggest the problem could be hj. i have no water softners , my basement is not finished as far as cieling , so i can see all the pipes , i checked them they have pipe brackets to support them about every 2 feet, would a bad washing machine solenoid cause it... the water company has been out here twice to check there side , they said everything is good on there side, i checked all the toilets to make sure there were no water leaks and made sure the flappers and internal parts were good . i just dont know what to check. but im up for any suggestions,,,,,,,,,,, THANKS.....
 