Hi -

I have a kinetico block salt softener about 12 y o. I currently have it isolated, as it recently flooded the kitchen. There is no obvious blockage in the overflow and water does drip through it, but when the machine is not isolated, water is flowing into the reserve tank at full pressure causing the water level inside to rise and rise until it floods over the top of where i put the salt in. I have tried trying to get it to manually regenerate, but it does not. The other thing that may be worth a mention is that, whilst investigating this problem, I have noticed that the open/close valves on the pipes to the machine leak when open.

I have tried my local service engineers, but am waiting since Friday for a call back - any ideas please?
 

phoebe

New Member
Messages
5
Reaction score
0
Points
0
Location
UK
thank you, i have tried removing and cleaning the float assembly. I replaced in the machine, and turned the water back on............. in doing so, I think i have discovered the problem. There is a split in the high pressure hose between the float assembly and the machine; could this be the reason that the machine will not manually regenerate also??? Could it be that there is not enough water pressure to get it to do so? And finally, do i need a kinetico specialist to replace it, or could a plumber do the job?

Thank you for your assistance ;-)
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Kinetico is sometimes very fussy about who they will sell parts to, so, even if you could fix it, you may not be able to get the parts. Not sure if this is generic.
 

Skip Wolverton

In the Trades
Messages
167
Reaction score
0
Points
0
Location
Ocala, Fl
Website
www.servicemagic.com
thank you, i have tried removing and cleaning the float assembly. I replaced in the machine, and turned the water back on............. in doing so, I think i have discovered the problem. There is a split in the high pressure hose between the float assembly and the machine; could this be the reason that the machine will not manually regenerate also??? Could it be that there is not enough water pressure to get it to do so? And finally, do i need a kinetico specialist to replace it, or could a plumber do the job?

Thank you for your assistance ;-)
If it's the hose that is split, you can replace it. It's a standard 3/8" high density tubing. If the split is close enough to a connection, just cut out the bad part for a quick fix and replace soon.
 

phoebe

New Member
Messages
5
Reaction score
0
Points
0
Location
UK
Thanks again - could you comment on whether the split would account for the machine not regenerating?
 

phoebe

New Member
Messages
5
Reaction score
0
Points
0
Location
UK
I am missing my softened water and cant afford £70+vat + parts call out fee. I can often fix things by myself ........ fingers crossed!!
 

big dripper

New Member
Messages
71
Reaction score
0
Points
0
Location
Ohio
Is the split on a hard plastic line or a flexible line. 3/8", 1/4"? What is the model number. You said you use a 'block salt type" unit? How big are these blocks (-+ 1/3 stone)?
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
The crack in the hose will not prevent the unit to going thru a regen, but will cause it not to draw brine which will result in hard water.
Really. How do you know that the leak isn't big enough to rob enough pressure to cause the water powered control valve to not be able to move the valving? Or, that the water flowing to the leak isn't preventing the valve from moving?
 

big dripper

New Member
Messages
71
Reaction score
0
Points
0
Location
Ohio
I wonder what your incoming pressure is? If the excessive pressure caused both leaks, then a pressure suppressor/regulator may be needed. Check what maximum pressure is permitted with the softener and what is coming in your home.

Hi -

I have a kinetico block salt softener about 12 y o. I currently have it isolated, as it recently flooded the kitchen. There is no obvious blockage in the overflow and water does drip through it, but when the machine is not isolated, water is flowing into the reserve tank at full pressure causing the water level inside to rise and rise until it floods over the top of where i put the salt in. I have tried trying to get it to manually regenerate, but it does not. The other thing that may be worth a mention is that, whilst investigating this problem, I have noticed that the open/close valves on the pipes to the machine leak when open.

I have tried my local service engineers, but am waiting since Friday for a call back - any ideas please?
 

Skip Wolverton

In the Trades
Messages
167
Reaction score
0
Points
0
Location
Ocala, Fl
Website
www.servicemagic.com
Really. How do you know that the leak isn't big enough to rob enough pressure to cause the water powered control valve to not be able to move the valving? Or, that the water flowing to the leak isn't preventing the valve from moving?
We're talking about a 3/8 line vs a 3/4 or even 1"inlet/outlet. There is no way for a 3/8 line to rob enough water to prevent the unit from starting a regen. If that were the case, anytime the unit was in a fill cycle, the customer would not have water flow in the home.
 
Last edited:

phoebe

New Member
Messages
5
Reaction score
0
Points
0
Location
UK
THank you for your help guys - I had to give in and call an engineer and am now £150 poorer.
The hose was split, and the fact that it was and that the vacuum was not maintained after the overflow caused the machine to not regenerate ????
Anyway - all fixed - hopefully I will be enjoying softened water again soon.

Thanks again
Phoebe x

Oh - and the water pressure in the daytime at the outside tap was 95 - he recommended that I fit a pressure control valve....... but wants a further £150..... not much chance of that then!!
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Take note that daytime pressures are usually LOWER than nighttime peak pressures. At least in the US, a regulator is required when the pressure exceeds 80#. If you do add one, you will probably also need an expansion tank (assuming you have a tank type heater, which you may not), to prevent the water pressure rising while the water heater raises the temperature and the water expands. A PRV makes the system 'closed' in that that expansion can't be passed back to the mains.
 

big dripper

New Member
Messages
71
Reaction score
0
Points
0
Location
Ohio
THank you for your help guys - I had to give in and call an engineer and am now £150 poorer.
The hose was split, and the fact that it was and that the vacuum was not maintained after the overflow caused the machine to not regenerate ????
Anyway - all fixed - hopefully I will be enjoying softened water again soon.

Thanks again
Phoebe x

Oh - and the water pressure in the daytime at the outside tap was 95 - he recommended that I fit a pressure control valve....... but wants a further £150..... not much chance of that then!!

Which hose was it? Can you describe it? Could you have replaced yourself?
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
We're talking about a 3/8 line vs a 3/4 or even 1"inlet/outlet. There is no way for a 3/8 line to rob enough water to prevent the unit from starting a regen. If that were the case, anytime the unit was in a fill cycle, the customer would not have water flow in the home.
As we see now the split prevented the regeneration as I said was possible and you said it wouldn't;

*************
The hose was split, and the fact that it was and that the vacuum was not maintained after the overflow caused the machine to not regenerate
**********
 
Top