I have a 1957 ranch with what I believe to be the original cast iron drain lines. When this was put in, why would they have used 4" pipe run vertically down from the toilets (only about 18" or so), then transitioned to 3" using a 4 x 3 elbow, then run the 3" to the 4" main line?

Why wouldn't they have just run 3" all the way from the toilet to the main and then transitioned to 4"?

Just curious more than anything...
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Hard to say what they were thinking, but to the best of my knowledge, it would never have beeen legal under any code to transition a waste line to a smaller size.

If this has been working since 1957 without problems, I would be the last one to recommend you go out and change it.
 

Smunderdog

New Member
Messages
29
Reaction score
1
Points
3
Location
Indiana
Thanks Jimbo - that is what I thought. Has been working most likely because the vertical 4" run is only 18" or so and then the horizontal 3" run is only another 18" before it hits the 4" main. At least it is that way on the one I'm redoing in the near future...

As part of my project of replacing a good portion of my cast drain lines, I'll be replacing the toilet drain with 3" for the entire run between the toilet to the main...
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
Hard to say what they were thinking, but to the best of my knowledge, it would never have beeen legal under any code to transition a waste line to a smaller size.

If this has been working since 1957 without problems, I would be the last one to recommend you go out and change it.

This is just information: It was a common practice to use a 4x3in closet bend with the cast iron systems. It is still legal under the UPC, the only place that you can do that, that closet bend is also close to a true 90deg. fitting. :)
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Give Shacko a cigar :D Closet bends can be 4" under both the UPC and the IPC And it was very common because it's darn near impossible to find a 3" CI toilet flange.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
But does anyone maintain that code allowed you to run a few feet of four inch pipe, then transition that to 3" pipe? I am not arguing that it works...he has told us that.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
4x3 bend

It not only works, but it is legal, and is the only way I have ever done it, other than when we were using all 4", then we used 4x4 closet bends. Plumbers who use 3" toilet risers, in my opinion, are more concerned about how inexpensively they can install it, rather than what is best for the customer.
 