I am trying to get a 1/2 hp 240V Grundfos well pump working on emergency power. All the other 120V circuits are working on the generator subpanel but the CFCI breaker on the portable generator trips when we start the well pump. Anyone know why this happens with the well pump?
Luc
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
Or perhaps the starting current of the pump exceeds the what the breaker can handle, what is the KW rating of the generator.

witch

Hello witch.
Thanks for answering. The generator rating is 8KW.

I took some reading of the pump circuit and there is a 3.8mA current on the ground when the pump is operating. My guess is that the 3.8mA added to the other leakage of the 120 circuits is tripping the 5mA trip sensitivity GFCI. (The pump circuit is in the generator subpanel with the other 120v circuits.)
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
It is the ground (bare copper wire) not the neutral, since there is a no neutral in 240V circuit.

I went to the pressure switch and plugged my ammeter in series between the incoming ground (bare copper) wire from the breaker and the bare copper wire going to the pumptec.
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
I do have a thread going in the electrical question forum. I started a new thread here because the pump was causing the problem. Removing the ground is not an option because it is to dangerous.

Thanks for all your help. We have a few options to solve the problem. We will see what we will do.
 

3m

New Member
Messages
74
Reaction score
0
Points
0
Location
NY
Have you checked the motor leads to ground with a ohm meter to see if the wiring insulation is starting to break down and leaking enough voltage that the gfci sees this as a short
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
Have you checked the motor leads to ground with a ohm meter to see if the wiring insulation is starting to break down and leaking enough voltage that the gfci sees this as a short

jnaas2,
We haven't checked that. What values should we expect for a Grundfos 1/2hp pump?
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
witch,

If we remove the ground wire, what protection will we have if we start the pump at the pressure switch and there is an electrical problem? We would get an electrical shock?
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
According to Franklin Electric:

New motor without cable: 20Megohm or more

A used motor which can be re-installed in the well: 10Megohm or more.

A new motor in the well with cables: 2Megohm or more.

Motor in good condition: 500,000 ~ 2Megohm or more.

Insulation damage, locate and repair: Less than 500,000.

A good 8KW generator should be able to run about 6 1/2hp subs.
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
We did the following measurements on the pump. The pump is 1/2Hp Grundfos. Submersible Motor control SA-SPM4. The cable lenght is about 300'. I don't know the pump model but it is over 10 years old.

Current phase A while running: 6.4-6.5A
Current phase B while running: 6.4-6.5A

Main winding resistance Yellow to black: 6.5 ohm
Start winding resistance yellow to red: 19 ohm

Insulation resistance for drop cable plus motor
1) Yellow to ground: 70 000 ohm
2) Red to ground: 70 000 ohm
3) Black to ground: 100 000 ohm
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
I would say your insulation is about gone. Either in the motor or in the sub cable. Ten years is a good long life for most sub motors.
 

Luc

Member
Messages
61
Reaction score
0
Points
6
Location
Quebec, Canada
I assume that a pump motor with less insulation means that it consumes more electricity. Any other negative effect other then tripping the GFCI?
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
When you get low ohm values on your meter through a motor, it's because some of that signal is escaping out into the water. That is wasted electricity.
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,302
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
A shorted motor that still runs uses a little more juice but, not much. If the amps are too high, then it will trip the overload, and the motor will have to be replaced.
 

Rugs

New Member
Messages
1
Reaction score
0
Points
0
Location
Vancouver
I've had the same problem with Grundfos pumps

I've used two Grundfos Redi-flo 2 pumps this past year. One rental and one that we just bought and I have the same problem, the GFCI breaker on the generator keeps tripping. The only way I've been able to get around it is to use a generator without a breaker.

I also tried calling the people at Grundfos and have had no luck.
 

dextercath96

New Member
Messages
2
Reaction score
0
Points
0
Location
philippines
Solar Generator, Is it environmental friendly equipment?
Ideal for camping or emergency power outages, the
Sun Power Port is a portable generator that when used
to its full potential will pay for itself in less than two

years.
In one day of full sunshine, the solar panel easily charges
the 12 volt (standard automobile) battery. An inverter
changes the DC current to AC. From there the electrical energy
is easily accessible to most standard 110 volt small
appliances used in North America. What are the advantages of

a solar generator? If you don't know, check out

sunpowerport.com. The featured generator will run most small

electrical appliances. It is great for camping or emergency

backup. No noise. No fumes.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks