PEX - Yea or Nay?

Do you like PEX?

  • Yes, PEX is a good product

    Votes: 14 100.0%
  • No, PEX is not a good product

    Votes: 0 0.0%

  • Total voters
    14

Users who are viewing this thread

Sixlashes

Plumber in Previous Life
Messages
82
Reaction score
0
Points
0
Location
Pensacola. FL
Another thread brought this issue up and I am looking for an experienced opinion. I am planning to use PEX to plumb my home utilizing a manifold for an all-home-run installation. I heard there was a problem with brass fittings. I was planning to use the crimp on rings with brass transition fittings.

Do the benefits of using PEX make it worthwhile? I was a copper only fan until folks I trust talked me into using PEX. What do you think?

Thanks.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Read this excerpt from the IPC. Quite a few plumbing inspectors have refused to allow and in fact made the installers tear out pex that did not comply. This includes but is not limited to Watts, viega, Rehau, Zurn and pretty much any pex tubing that uses an inserted fitting and a crimp ring, band or sleeve.

Reference: IPC 605.5
Category: Water Supply and Distribution
Subject: Materials, Joints and Connections
Code Text: Pipe fittings shall be approved for installation with the piping material installed and shall
conform to the respective pipe standards or one of the standards listed in Table 605.5. All
pipe fittings utilized in water supply systems shall also conform to NSF 61. The fittings shall
not have ledges, shoulders or reductions capable of retarding or obstructing flow in the
piping.
Ductile and gray iron pipe fittings shall be cement mortar lined in accordance with
 

Jay Mpls

Master plumber
Messages
95
Reaction score
1
Points
0
Location
Minneapolis
I am in! I would run with Veiga or Wirsbo(Uponor).If You have any questions about the brand of PEX you wish to use I would give a call to your local plumbing inspector and run it by him/her.
 

crater

New Member
Messages
49
Reaction score
0
Points
0
one year old house--> home-run system using Pex with crimp rings NO LEAKS from the very start. fingers crossed
Pressure test lines before you cover them.
Places that disallow Pex should really get with the times. The code mentioned should include "the 1000's of standards depending on the inspectors mood" and would only pass some space age material not yet handed down to us by little green men from mars.
Don't get me wrong codes are code and we may have to follow them, but I'll bet there is no one person on this forum that hasn't said that one or another code just doesn't make any sense. These are the very ones that the trades try to get corrected but still slip though the cracks at the "inspectors convention" every year. Until the book gets changed it'll take a engineers stamp to override the code, stupid or not.

Job security I think
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Well that little excerpt from the IPC has and will continue to cause problems. Local inspectors do not have the authority to override a code unless the ammendment is more stringent, not less. Even the State inspectors can't give a pass on that one. I've had plumbers assert that if they up size the pex by one pipe size that covers it, but again the code itself does not say that. The code says what it says. If you crimp Watts, Viega, Zurn and then cut the joint laterally you can plainly see a ledge where the fitting inserts into the pipe, and the code strictly prohibits this. Is it stupid? Probably. But again, I would hate to rough an entire house and then have to tear it all out. Even if the local inspector passed it, if it ever came down to a law suit I would be liable, not the inspector. Never assume that because the manufacturer puts this stuff out there that is must be ok to use.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
code

That would be an assine interpretation of the code. That would mean that polyethylene pipe could not use the common barbed fittings, even though they, and the PEX fittings, have passed the IAPMO and other certification tests.
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
Plumbers love it because its so damn easy running basically hoses through walls. They can leave their chalk line and level in the truck. Plus they don't have to clean and flux, then heat joints inside wood studs. I had my house plumbed with it because I knew it would save time. The only problem that I've had with it is expanding it. The tool to crimp the bands is expensive, and is difficult to fit into tight areas, which are typical with doing retrofits.

This is the same house that the "professional" refused to install a PRV and I found out from the utility that the street pressure is over 150psi. At least I know the stuff has been tested (along with my refrigerator and the rest of the house!).
 

Sixlashes

Plumber in Previous Life
Messages
82
Reaction score
0
Points
0
Location
Pensacola. FL
I see the issue with the reduced internal cross section of the fittings. However; the cross section of the riser tubes for sinks are almost always 1/4". I am all about not cutting down flow. I will indeed call the local inspector to find out his interpretation. Good point that just because the supply house sells it, doesn't mean all of the surrounding county inspectors will pass it.

Has anyone seen any failures with the crimp rings? I remember reading about an issue with the fittings being able to spin after installation. Or issues with the PEX itself? I plan to use drive-in insulators in studs and joists to keep it from possibly chafing. I have access to all sizes of the Zurn crimpers with the go no-go gages.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
What can I say? You read it, I read it. It says what it says. I think it's an assinine interpretation also, however it ain't up to us to interpret. Remember this is for supply and distribution piping. Typically insert fittings are used before the supply piping begins. Supply tubes to fixtures have always been exempt in Flow calculations due to the short distance. Nominal passage through a 1/2" pex fitting is about 11/32 nds of an inch compared to 1/2" swett copper, plus the ledge. So you tell me. If you were an inspector would you let it go?
 

Attachments

  • plumbing shop 054.jpg
    plumbing shop 054.jpg
    19.7 KB · Views: 1,178

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
I Dunno...
You tell me...

Standards and Approvals
WaterPEX® is manufactured in accordance with American
Standard Testing Methods F-876 and F-877 to SDR-9
dimensional standards. It is listed by the National Sanitation
Foundation NSF-61 for use in potable water systems.
WaterPEX® is also listed by the International Conference
of Building Officials (ICBO), the International Association of
Plumbing and Mechanical Officials (IAPMO) and carries the
Uniform Plumbing Code symbol. WaterPEX® is tested and
certified to the Canadian Standard Association (CSA)
standard B137.5. WaterPEX® fittings and pipe are not
compatible with polybutylene pipe or with other cross-linked
pipes and fittings not made to this SDR-9 standard.
it out for fit and appearance, then crimp each connection
for permanence.
http://www.watts.com/pdf/IS-WaterPEX.pdf

Sounds like the IPC might be cotradicting itself...
Maybe you should bring it up for the next round of revisions...
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Well ya. All this crap needs to be put up for revision. It's the reason I have been so against the IPC since we adopted the damn thing. It's full of stupid stuff. I really wish that every State would adopt the same code with local revisions. Someone (not me , I have enough crap on my plate) needs to take all of the existing codes and blend them into one sensible, coherent piece of legislation that incontrovertable.
 

Bill Arden

Computer Programmer
Messages
584
Reaction score
0
Points
0
Location
MN, USA
Website
www.billarden.com
I've not heard of any problems with regular PEX and brass fittings.

As I understand it the problems were with AL barrier PEX

edit: I thought the expander tool that they used on PBS looked easy to use, but expensive.
They put a larger ring of PEX over the PEX and then used a tool to expand it before putting it over a barbed end.
 

crater

New Member
Messages
49
Reaction score
0
Points
0
funny you mention that the fittings spin after crimping. I myself said there was no way that this won't leak (because murphy follows me like my shadow) my fittings spun,not loosely but never the less they could turn. The only problem I had once was with a quick connect Pex fitting. It leaked because I didn't have it all the way on. The kind that just slip onto the end of the tube. My advice; don't use Quick connect fittings, the're way more expensive and seem not to instill the confidence that they won't leak, plus I'm not sure about pressure they'll handle.
 

Basement_Lurker

One who lurks
Messages
664
Reaction score
1
Points
0
Location
Victoria, BC
Unless you are doing a huge b&t pex system, the small pressure drop caused by the reduced diameter of the crimp fittings is hardly a factor. And yes a crimped fitting can spin if you twist it hard enough...if you think about it, you'd understand why...the crimp ring forces the tubing down onto two grooves which press into the tubing...so you may be able to spin the tubing as the grooves are circular...but you won't be able to pull the joint apart!
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
Well ya. All this crap needs to be put up for revision. It's the reason I have been so against the IPC since we adopted the damn thing. It's full of stupid stuff. I really wish that every State would adopt the same code with local revisions. Someone (not me , I have enough crap on my plate) needs to take all of the existing codes and blend them into one sensible, coherent piece of legislation that incontrovertable.

Years ago NY State had a nice plumbing code that gave a simple design method for sizing supply lines based on cumulative fixture units. I designed all the plumbing for a 44 unit hotel in about an hour. With the current IBC you need a friigin' computer program to figure it out, even for a small job.
 

Kingsotall

Plunger/TurdPuncher
Messages
1,238
Reaction score
1
Points
0
Location
Flagstaff, AZ
I've not heard of any problems with regular PEX and brass fittings.

As I understand it the problems were with AL barrier PEX

edit: I thought the expander tool that they used on PBS looked easy to use, but expensive.
They put a larger ring of PEX over the PEX and then used a tool to expand it before putting it over a barbed end.

Wirsbo uses this method. Depending on which expander tool you use it can be expensive.
 

pbaker

New Member
Messages
6
Reaction score
0
Points
0
pex problems

I have had 3 failures with pex fittings over the last 7 years. Each of them at the pipes coming in from a well to the water heater. The first was the T fitting coming into the water heater. The next was the 90 coming out of the water heater. Each of these we caught with minimal water clean up. Fortunately we have mostly scored & stained concrete slab, too. The last one was the doozie. It was the 90 going into the water heater. It flooded 70% of the house. I came in and there was 2" of water on the kitchen floor. I heard it in the laundry room, waded to it and there was a jet stream pelting the opposite side wall. I told my wife, "I think it is time to get the manufacturer to see this."

After contacting Zurnpex, shipping the fittings to them and trying to sort it all out, I received a letter last month that the fittings were not theirs, but Dura-Pex. I contacted NIBCO - Dura-Pex and their representative sent me to an insurance company. I was not even talked to by a claims adjuster, only a "Litigation Examiner" who never asked any questions and simply denied the (was not even) claim saying that Consolidated's materials were excluded from their policy. I work in construction, so I know how many unexpected variables can cause failures like this, however, everything I have checked seems to go back to fitting failure... plain and simple. I am not sure of anyone's expertise with this, but I would greatly appreciate any direction and advise offered.
 

99k

Radon Contractor and Water Treatment
Messages
460
Reaction score
2
Points
0
Location
Fairfield Co.,Connecticut
Website
www.78radon.com
I use the Propress / Viega tool. I presently just crimp copper tubing, however, I can buy a jaw for 3/4 PEX for $100.
Does anyone have experience with the viega PEX. It appears to be a much more robust crimp and looks very similar to a crimp used on a hydraulic line.
Comments?
 