I recently replaced an electric water heater with a new one.
The old water heater had 4500 watt elements on a two pole 30 amp breaker
The new water heater has 5500 watt elements. the problem is periodically the breaker in the panel is tripping. Acording to the water heater specs the amperage should only be 22.9. Is it a problem if I replace the 30 amp breaker with a 40 amp breaker. I would run new # 8 wire to the water heater or should i just replace the existing 30 amp breaker with a new one.
The old water heater had 4500 watt elements on a two pole 30 amp breaker
The new water heater has 5500 watt elements. the problem is periodically the breaker in the panel is tripping. Acording to the water heater specs the amperage should only be 22.9. Is it a problem if I replace the 30 amp breaker with a 40 amp breaker. I would run new # 8 wire to the water heater or should i just replace the existing 30 amp breaker with a new one.