Schedule 40 PVC vs. Schedule 40 Foam Core

Users who are viewing this thread

ROSSBYINGTON

New Member
Messages
2
Reaction score
0
Points
0
My wife and I are building a house. The builder(gen'l contractor) was instructed to use Schedule 40 PVC and now we see there is Schedule 40 Foam Core in the house (including the exterior waste lines). The walls are not yet closed. The builder & plumber said that Foam Core is they typical product of choice and that we shouldn't worry about it. I called Charotte yesterday and asked the rep. if he was building his home what would he use and the answer was Schedule 40 PVC.

What do you think? Are the two pipes of equal quality? Are we being to picky? This is an expensive custom house that, until up till now, has been built beautifully (both structurally and visually).

Thank you in advance.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
pipe

Schedule 40 is a measurement, not the pipe's quality. All sch.40 pipe will have the same i.d. and o.d. which means the wall thickness will be the same. That has nothing to do with HOW the pipe is made, i.e. solid core or foam core. We do not use PVC drain lines here, but where it is used, foam core seems to be the material of choice for drain lines. But it is not a "pressure" material so it is not used for supply water lines. If it were a problem for you, your specification should have called for scheduler 40 pressure rated piping.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
I'd call the manufacturer for thoughts. My gut feel is that the foam core stuff is more susceptable to getting crushed underground under adverse conditions - it isn't as strong (but might be more flexible which could help - I don't know, this is a guess). Those shouldn't happen, but could. Inside the house, I wouldn't have big problems with either, it is only outside I'd have to give it a second thought.
 

cab

Member
Messages
30
Reaction score
0
Points
6
Location
Wisconsin
Not sure but I hear it is against code in WI to use foam core pvc in the dwv lines....
 

ROSSBYINGTON

New Member
Messages
2
Reaction score
0
Points
0
Gentleman,

Thanks for the help. I called the manufacturer again today and the tech was extremely confident that the foam core would work fine. I also spoke to the local inspector who was also sure it would work properly.

My frustration is that the foam core was not specified but installed. Do I win the battle (by having them spend the time and money replacing it) and possible lose the war when the project grinds to a halt. GC omits to the mistake but has not really come up with a solution.

Dazed and Confused in DC who now knows more about PVC pipe than I ever thought I would.

Ross
 

Lancaster

New Member
Messages
163
Reaction score
0
Points
0
Here's how I see it.You could request the materials price be reduced by the difference between the pipe prices.But if you did that,you would probably have to absorb the recent large increases in PVC cost.So it would basically wash out anyway.
I say no harm,no foul,let it slide.
 

Tjbaudio

Member
Messages
167
Reaction score
0
Points
16
Location
Las Vegas NV
As long as there are no long unsupported lines the your fine. This would hold true for any material. I have the foam core stuff and it is not a problem. If the building inspector is happy let it go. It will not affect the value of the home any way.
 

fozzy12

New Member
Messages
27
Reaction score
0
Points
0
Location
North of Detroit, MI
Foam core PVC

Let it slide, it isn't affecting anything. The GC admits it was a mistake, he knows you're paying attention. He will probably be a little more careful in the future. No sense starting a needless war if you like what he's done so far.

Eric
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Let it slide inside, but check the city code to see if you can use it outside underground.



Jason
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
The only performance issues I've seen with the product is how you have to lip the ends of the pipe with glue and cleaner when preparing the solvent weld joining method to prevent an air test failure.

Meaning, if you don't consider this practice you'll have problems with getting air tests to properly hold for inspections, due to the fact that air can travel through the piping walls.

I guarantee your plumbers did this to protect this situation from happening, otherwise they know the fix. Tear it out!

When foam core came out eons ago, we were told to make this a common practice in order to get air tests to hold 5 pounds of air.
 

Rdtompki

New Member
Messages
115
Reaction score
0
Points
0
Location
Iowa
I'm a bit confused about the part of the original question that talks about the PVC being inside the "walls" or is the original question only referring to drain and waste in the walls vs. potable water?

Rick
 

BAPlumber

Plumber
Messages
227
Reaction score
2
Points
0
Location
Vashon, Washington
My wife and I are building a house. The builder(gen'l contractor) was instructed to use Schedule 40 PVC and now we see there is Schedule 40 Foam Core in the house (including the exterior waste lines). The walls are not yet closed. The builder & plumber said that Foam Core is they typical product of choice and that we shouldn't worry about it. I called Charotte yesterday and asked the rep. if he was building his home what would he use and the answer was Schedule 40 PVC.

It sounds like the GC did what he was instructed. He used Sch. 40 PVC. If he was instructed to use Sch. 40 Solid Core PVC and didn't, then there may me a problem. The pipe will work fine, it just isn't what was contracted for.
 

Tattors

New Member
Messages
2
Reaction score
1
Points
1
Location
North Carolina
when a snake tears away, or rubs, while cleaning; then the exposed foam will be exposed for failing and one will wish they had not shaved a few bucks off for a better builder bottom line..... Foam core is a time bomb that has solved the problem of PVC line invincibility. sweet
 

Holeshot

New Member
Messages
16
Reaction score
1
Points
3
Location
California
when a snake tears away, or rubs, while cleaning; then the exposed foam will be exposed for failing and one will wish they had not shaved a few bucks off for a better builder bottom line..... Foam core is a time bomb that has solved the problem of pvc line invincibility. sweet

Wow! Only one person knew what's up with foam core vs solid core!
 