Extending ungrounded circuit

Users who are viewing this thread

muzz

New Member
Messages
21
Reaction score
0
Points
0
I have question about a lighting circuit in my house. It is an older 2 wire 15 amp with no ground.
I want to add one receptacle to this circuit to be located on the wall outside of the bathroom since I have everything in the bath opened up for a remodel. This circuit will also serve two light fixtures in the bath. We have a house that was originally built in the 50's, with no overabundance of outlets in the house, but over the years we have added them. I am not sure about this situation though. Is it ok to mix lighting and outlets; especially with no ground? It is the easy way to do it, but I want to do it right.
It would be easy enough to add one from the bath circuit, but I am fairly certain that is a no go.
How important is a ground on a lighting circuit? My living room has the same situation; is there anything inherently bad about no ground wire. What seems odd is that a new breaker was added in the panel for the bath, and when we checked the circuit for the living room, there is a ground wire at the panel.

One more question, I think I know the answer, but here goes anyway--When extending a circuit thats wired with 14 gauge wire, is it ok to wire the extension with 12? (15 amp circuit)
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
It is OK to add #12 wire to a 15 Amp circuit.​

It is also permissible to have receptacles and lighting fixtures on the same circuit.​

If I had to extend an ungrounded circuit I would find the first receptacle on the circuit and replace it with a GFCI receptacle, with the following part of the circuit connected to the load terminals of the GFCI receptacle.​

I would do the same thing on the bathroom receptacle circuit.​
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
It is NOT okay to feed 12 gauge off of a 14 gauge circuit.
Ever.
Code-wise, or common-sense safety-wise.


It is okay to mix lighting and receptacles.


It is not okay, code-wise anyways, to extend a circuit, without bringing the whole thing up to code. Ungrounded circuits are only allowed because they're "grandfathered" - i.e., they were okay at the time they were put in. If you modify it, you have to upgrade it to current code. How else is the extension going to meet current code, which it has to since it's being done now?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
wires

It is NOT okay to feed 12 gauge off of a 14 gauge circuit.
Ever.

Now you tell me. And here every house I have had for the past 30 years had all 12 gauge wires for every circuit, including 15 amp ones. So i guess you will have to tell me why it is "not okay". And be convincing.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
It is NOT okay to feed 12 gauge off of a 14 gauge circuit.
Ever.
Code-wise, or common-sense safety-wise.


It is okay to mix lighting and receptacles.


It is not okay, code-wise anyways, to extend a circuit, without bringing the whole thing up to code. Ungrounded circuits are only allowed because they're "grandfathered" - i.e., they were okay at the time they were put in. If you modify it, you have to upgrade it to current code. How else is the extension going to meet current code, which it has to since it's being done now?

Please cite the code paragraphs that prohibit extending a #14 (15 Amp) circuit with #12 wire, and that require that grandfathered ungrounded circuits be upgraded to existing code if modified as in by extending it.

I suggest that 250.130 including 250.130(C) permits the extension without upgrading the whole circuit, and 406.3(D)(3) describes the approved method of adding a GFCI to a circuit without an equipment ground.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I

learn

something

new

every

day.

bigdoglittlechick.jpg


And it takes a big dog to admit it.

Notice that the chick is the little one here lol
 

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
It is NOT okay to feed 12 gauge off of a 14 gauge circuit.
Ever.
Code-wise, or common-sense safety-wise.

True, 'common sense' may dictate not using #12 on a 15amp circuit, but it is not a Code violation. Yes, someone may, in the future, see the #12 wire and assume it's a 20amp circuit, but then they should read 90.1(C) and the definition of a "Qualified Person".
 

joe in queens

New Member
Messages
35
Reaction score
0
Points
0
Here in NYC it's a CODE REQUIREMENT that #12 be used on 15A circuits, lighting and otherwise; #14 on a 15A circuit will be red tagged. I still haven't found anyone - even NYC inspectors - that can tell me the logic for this.
 

muzz

New Member
Messages
21
Reaction score
0
Points
0
ok, so I guess that I can run the extension with 12 gauge, but code says that I have to put in a gfi outlet.

Any comments on these--

How important is a ground on a lighting circuit? My living room has the same situation; is there anything inherently bad about no ground wire. What seems odd is that a new breaker was added in the panel for the bath, and when we checked the circuit for the living room, there is a ground wire at the panel.

Would the ground wires have not been used purposely?

Thanks for all the answers the last couple weeks.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
The purpose of the ground wire (Equipment Grounding Conductor) connected to metal parts of the electrical system, and to equipment connected by a grounding plug, is to trip the circuit breaker if the grounded part is accidently energized; thereby protecting against fire hazards and protecting those who might contact that potentially energized part.

The purpose of the Ground Fault Circuit Interrupter (GFCI) is to provide additional protection on high-risk circuits where a person has a higher risk of contacting a potentially energized piece of equipment (such as a hair dryer or washing machine) while touching another grounded piece of metal such as a faucet. The GFCI is supposed to trip at a low current (less than 0.006 Amp) that would not be fatal to a human.

Absence of a ground is a lower risk in places where it is unlikely that a person will come in contact with an unintentionally energized metal part, such as in a ceiling-mounted lighting fixture.

Absence of a ground and/or GFCI is a significant risk around a piece of equipment such as a washing machine, which has a lot of potential for being accidentally energized and is in the vicinity of a grounded faucet that can be reached by an operator of the equipment.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
Just to clarify -

I didn't think it was wrong to use 12 gauge on a 15 amp circuit - in fact, it's what I'm used to, since I'm in NYC where everything is 12ga.

(Joe - FWIW - the rationale I was given, years ago, is that NYC apartments get a lot of illegal extensions added on, people overloading circuits by running new branch extensions, etc... so they like to have some margin of safety built-in. Begs the question, though: why aren't 20 amp circuits required to be 10 ga? and so on... In the end, like so much else in the city codes, the real answer is, "just because".)

What I did think, was that you can't increase the size of the conductor, further along the circuit, from what you start with. Kinda like plumbing drain lines, where you can't go to a smaller pipe, further downstream?

And I coulda sworn I'd read something, in some sparky discussion online somewhere... I guess the main lesson is that I'm no brainiac when I'm insomnia-posting.

So I'll shut up now, lest I repeat the foot-mouth process, lol.


Oh - the other thing - the gripe I thought I had with my sparky - was about the need to update the branch you're tapping into.

But thinking about it... I don't think he ever said it was code-required. Just "this is the better way to go about it". Since we're usually dealing with open walls... it's probably just plain easier.
 

KD

New Member
Messages
207
Reaction score
0
Points
0
It is always OK to use larger wire, say #12 or #10 on a 15 amp circuit. It is NOT OK to use smaller wire.
If you are adding new wire, "extending a circuit", you must use new 3 wire grounded cable, or wire in conduit and it must be grounded. You shall not connect new wiring to an old two wire system. GFCI protection does not change this rule.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
You shall not connect new wiring to an old two wire system. GFCI protection does not change this rule.
Would you please post a quote to this rule from any code that is published.

Here is what I have found in the National Electrical Code and it disagrees with you;

406.3(D)(3) Non–grounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.†An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected†and “No Equipment Ground.†An equipment grounding conductor shall not be connected between the grounding-type receptacles.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
If you are adding new wire, "extending a circuit", you must use new 3 wire grounded cable, or wire in conduit and it must be grounded. You shall not connect new wiring to an old two wire system. GFCI protection does not change this rule.

250.130 says in part : ". . . For replacement of non-grounding receptacles with grounding type receptacles and for branch circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C)." (emphasis mine)

250.130(C) lists 5 different permitted points to connect the equipment grounding conductor of a branch circuit extension.
 

KD

New Member
Messages
207
Reaction score
0
Points
0
I stand corrected. Our local AHJ has a more strict rule. It looks like, per the NEC, you could protect all circuits with GFCIs and have every receptacle in a 2 wire house be replaced with a three wire modern receptacle with little no grounding tags on them. It is a trade off--install GFCIs which makes things safer, and you can use 3 prong receptacles.
 

muzz

New Member
Messages
21
Reaction score
0
Points
0
I still have one unanswered question, if you could help. I don't expect anyone to know why, but maybe you have run into this before. When installing the new breaker for the bath, I checked the circuit for the living room, and it does have a ground wire, but none of the receptacles do. Could it be possible that they just weren't used, maybe cut off at the first fixture?
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
I'd love to hear the Pros' answers, but my amateur answer would be -- anything's possible. If you can find that first living room receptacle, you'll have the answer. Tracking down and mapping a circuit in a house is an interesting, funny, and sometimes humorous exercise, but I've done it for every house I've owned, and never regretted the time spent doing it.

If you're really lucky, the ground wire at the first outlet will still be usable (not snipped off short), in which case you can install a grounding receptacle there. Or, there may be enough slop in the cable to pull more into the outlet box and expose a usable length of ground. The cables connecting downstream outlets may or may not have ground wires, but keep tracing, and replace those ungrounded receptacles which have valid ground wires available. You might also consider replacing the head receptacle in the chain with a GFCI receptacle for added safety.

I had a similar experience with a dryer circuit, where the neutral wire was snipped (you used to be able to use the ground as neutral, I think). I was installing a new dryer with a 4-prong plug, and wanted to use all 4 wires (2 hots, neutral, ground). I gave the cable an experimental tweak and drug (I live in the South) another foot or so of cable into the box and I was good to go.
 
Last edited: