I'm down to the wire on getting my 4- plex lowboy gas water heaters switched to 50 gallon electric and I'm checking the load calculations one more time. I can't seem to find the online calculator i used in the past and the mike holt calculator shows a 100 amp serv no matter what i put in.

Here is what I have. 90 amp main in each unit. 1100 sq ft. each unit with Electric range, Dryer, Fridge, DW, disposal. Heat is gas furnace and there is no AC. The last time i ran the calcs adding an electric water heater was no problem but I would like to confirm that.

Thanks for all the great help on this forum. HS
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
230.79(C) One-Family Dwelling. For a one-family dwelling, the service disconnecting means shall have a rating of not less than 100 amperes, 3-wire.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I'm down to the wire on getting my 4- plex lowboy gas water heaters switched to 50 gallon electric and I'm checking the load calculations one more time. I can't seem to find the online calculator i used in the past and the mike holt calculator shows a 100 amp serv no matter what i put in.

Here is what I have. 90 amp main in each unit. 1100 sq ft. each unit with Electric range, Dryer, Fridge, DW, disposal. Heat is gas furnace and there is no AC. The last time i ran the calcs adding an electric water heater was no problem but I would like to confirm that.
I don't get what the question is. Is there one?
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
heater

You haven't told use the element wattage of the heater(s). If they are resiential units with 4500 watt, non simultaneous operation then the draw is approximately 20 amps with a 30 amp breaker.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I don't know if the 90 amp service is adequate. But I wonder why you are switching the WH from gas to electric?? In most areas, it seems that it costs a lot less to run a gas unit.
 

HammerSlammer

New Member
Messages
68
Reaction score
0
Points
0
Location
Colorado
Even that, at 1100ft/sq you should be fine, especially considering no A/C.

Thanks Pete. That's what i needed to know. I got a little tongue tied describing.

I don't know if the 90 amp service is adequate. But I wonder why you are switching the WH from gas to electric?? In most areas, it seems that it costs a lot less to run a gas unit.

Thanks Jim. I have lowboy gas, the ones they don't make anymore. Even at that they were dug into a hole in the crawler and i couldn't get them to pass today anyway. So I'm comming out of the crawler and can't seem to work out anything is gas so I'll put these electrics in and maybe in 6 years I'll have more options... Our gas doubled and electric stayed at about 7.5 cents so I think I'll be alright for a few years.

The wording of this section is the same today as it was in the 1984 code cycle.

Thanks JW,

I don't know but I know I was there when all the inspections was done in 1985 and generally speaking our requirement have always been fairly strict. That's why I'm trying to keep my ducks in line. I can anticipate an inspector who might say " Bring the whole building up to current code" because i'm changing a water heater.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
At 7½ cents per kwh for electric, an electrice WH is not a bad choice. Our electric is 16 cents!
 

HammerSlammer

New Member
Messages
68
Reaction score
0
Points
0
Location
Colorado
7.5 cents???????????? :mad:

Actually 6.9 cents but there is the 22 cent per day access so I figure a little more. That is about what it was in 1985. Hope they can hold out for a few more years... Our gas is 60 cents per ccf with a 30 cent per day access. That is about double from 2 years ago.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
1100 sq ft. each unit with Electric range, Dryer, Fridge, DW, disposal. Heat is gas furnace and there is no AC.

1100 x 3 = 3300
Small appliance and laundry 4500
Range 12,000
Dryer 5000
Fridge is included in the small appliance circuits
Dish washer 1200
Disposal 750
Total 26,759

First 10,000 at 100%

16750 x 40% = 6700

6700 + 10,000 = 16,700

16,700/240 = 69.58

Now lets add a water heater = 77.09

Change the 90 amp breaker to 100 and be done with the job.
Make sure that the SE cable is either #4 copper or #2 aluminum
 

HammerSlammer

New Member
Messages
68
Reaction score
0
Points
0
Location
Colorado
1100 sq ft. each unit with Electric range, Dryer, Fridge, DW, disposal. Heat is gas furnace and there is no AC.

1100 x 3 = 3300
Small appliance and laundry 4500
Range 12,000
Dryer 5000
Fridge is included in the small appliance circuits
Dish washer 1200
Disposal 750
Total 26,759

First 10,000 at 100%

16750 x 40% = 6700

6700 + 10,000 = 16,700

16,700/240 = 69.58

Now lets add a water heater = 77.09

Change the 90 amp breaker to 100 and be done with the job.
Make sure that the SE cable is either #4 copper or #2 aluminum

Thanks JW. I got the breaker changed out and every thing done and inspected today. Went pretty smooth and I'm happy to get one appliance out of the crawler for good. Three more to go. Thanks for all the help. HS
 

HammerSlammer

New Member
Messages
68
Reaction score
0
Points
0
Location
Colorado
I got all 4 installed, working, and inspected. Looks like electric is running about the same $ for these appliances as the gas for this area, ($.07/kw), with about three people in each unit. I suspect that larger families would make a difference.

Thanks again for all the help.
 