Just installed my new Kohler Highline Class Five toilet. The flapper valve closes instantly upon release of flush handle not allowing enough water to flush properly. Only a small amount of water returns to bowl. The temporary solution is to hold down the flush handle for approx. 3 seconds to get a good flush.

Have spoken with Kohler and have not been able to resolve the problem.

Has anyone had a similiar problem with the class five flushing system?
 
Last edited by a moderator:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
As Terry pointed out, it is probably flushing the 1.6 gallons, and doing it almost like a "gulp". This is how they work. Many 1.6 gallon toilets using the large flapper design that Kohler calls Class 5, flush very well. The flush "looks" and "sounds" different than what you are used to.

Are you actually having poor flush performance?
 

dfhsah

New Member
Messages
2
Reaction score
0
Points
0
Location
Massachusetts
Problem with my Class Five Kohler toilet.

The toilet only lets out approx 3 quarts of water and the bowl only recovers about 4 inches of water measured from the absolute bottom of the bowl.

The tank refills to the 1.6 gal mark but never discharges the correct amount.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Again, does the toilet dispose of the waste? They do flush with a "gulp" and compared to older toilets which in truth probably flushed MORE than the specified 1.6, probably seem skimpy.

Some of these "class five" type of toilets have a low water spot. You can confirm the water spot by taking a gallon or so of water and very slowly pouring it into the bowl. If the water level rises and stays there, then you do have a refill problem. If it stays at the same level, that is your design water spot.
 

SteveW

DIY Senior Member
Messages
1,282
Reaction score
22
Points
38
Location
Omaha, NE
Problem with my Class Five Kohler toilet.

The toilet only lets out approx 3 quarts of water and the bowl only recovers about 4 inches of water measured from the absolute bottom of the bowl.

The tank refills to the 1.6 gal mark but never discharges the correct amount.


Have you actually measured the amount of water used?

The mark on the tank is not the 1.6 gal mark - as has been said, modern low flow toilets do not discharge their entire tanks when they flush. In other words, the tanks hold more than 1.6 gal. They use the "head pressure" of having more water than the flush capacity to move the water more forcefully into the bowl.

If you want to really check how much water is being used, mark the tank at the level it refills to (not necessarily the same as the permanent mark on the inside of the tank). Then shut off the water to the tank, flush the toilet normally, and see how much water it actually takes to refill.
 

Larry0400

New Member
Messages
6
Reaction score
0
Points
0
Considering Kohler highline

Does anyone know if this is a decent toilet? I like its looks, don't like the looks of the Toto and was considering this for my 23 year old house. The run from the toilet to the septic tank is about 50 feet and I am sure the slope is minimal code in the drain pipe. Any ideas.
Thanks
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Toto makes probably 50 different models...you hate them all?

The total water use on a toilet is not only the amount that gets dumped quickly while the flapper valve is opened, but most toilets also overfill the bowl some, and nearly none empty the tank during a flush.

Kohler isn't on my good list, but then again, I don't do this for a living. My personal experience with them has not been good.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Which specific model are we talking about?
Class 5 flush?
Pressure assisted?

IMHO they are all lesser quality than the Toto.
 

Larry0400

New Member
Messages
6
Reaction score
0
Points
0
Kohler vs. Toto

I visited a Toto dealer. Great showroom. It isn't that I dislike all the Toto's, just wasn't thrilled with the appearance of what the fellow was showing me. Most likely this was because I mentioned that I have exactly 11 inches rough in (wall to center of the bolts), The dealer suggested some skirted models with adapters that were made in various lengths for 3 models- the Gwenaviere, the Soire and one other single piece toilet that I can't remember the name of. Each had the latest features including Saniglaze and a swirling flush system. I think it looks like it would rinse the bowl as well as any other toilet, as this was one of my concerns. Any thoughts?

I might be able to use a 12 inch rough in but it will be tight, as Toto allows only 3/4 inch clearance inside the 12 inch spec, and I might just fit it snug against the wall, but it could be a problem by only 1/4 inch.

The models with different rough in adapters didn't impress me because they had a right angle connection from where the toilet connected to the pvc adapter and it looked like it might act as a restriction. I thought restrictions were something Toto was trying to minimize by the saniglaze. Doesn't the right angle pvc adapter for 10 inch and 14 inch rough ins defeat all the rest of the Toto engineering? I have a hard time understanding why this wouldn't cause problems. I have also read reports of dripping noises in these models. Any ideas on these issues?

I wasn't too impressed with the plastic seats on the Toto's. Do most people think it is good?

The Kohler called for a 1 inch space behind on a 12 inch rough in, so I thought it might fit my space better. I also liked the styling better on the Kohler, but everyone on here strongly recommends the Toto's and I don't hear much enthusiasm for the Kohler products. Are any of the Kohlers worth considering?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
With 11", sometimes you can fudge things, sometimes you can't. The unifit adapter, being cast in plastic, is much smoother and engineered curves than you can do in an all porcelain cast toilet...I've got several - they work very well. The skirted versions might require moving the water supply line, since the skirt does hide more wall behind the toilet. I wouldn't let that be a deciding factor. you could try it with the stock 12" unifit, and if it didn't fit, then pick up the 10" one and be assured it would fit. I have a Carlyle and a Vespin in my home.
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
If you like the looks of the Highline, then why not buy it?

The spec on the Toto Drake, which is similar in styling to the Highline says 1-1/8" behind the tank.
We set them at 11" all the time.
 

Larry0400

New Member
Messages
6
Reaction score
0
Points
0
Terry- How good is the Kohler HighLine? From what I have read on your site, the Totos you seem partial to the Totos.
I was all set to get the Toto Gwineth (new dual flush and saniglaze) but at the dealer, when I pushed it against the wall in the distance from the wall to the bolts was exactly 12 inches. Toto's diagram was wrong- it showed the 12 inch rough in included a 3/4 inch space behind the tank to the wall- not so. Perhaps it exists between the sides of the tank and the wall, because they are curved, but the absolute closest distance you can set it from the wall to the bolts is 12 inches with the center back right against the wall.

Thanks for the reassurance on the plastic adapters not being a problem. I will probably try a Toto skirted model. Most likely Guinevere. What do you think of that model?
 
Last edited by a moderator:

Larry0400

New Member
Messages
6
Reaction score
0
Points
0
Almost forgot-
Terry, Thanks for the suggestion on the Drake. I know everyone loves it. I didn't get a chance to see it, as I was concentrating on the Saniglazed units. I'll take a good look at it. The folks in the local supplier were pushing the latest gratest models. Wonder what you think?

The CEFIONTECT versions of the Drake are CST744SG and CST744EG
 
Last edited by a moderator:

Mort

New Member
Messages
83
Reaction score
0
Points
0
Location
CA
FWIW, I just had three Soiree units installed and couldn't be more pleased. The Soiree, Guenevere and Lloyd appear to be pretty close to the same configuration. The unifit adapters were the deciding point as all three rough ins were different in my house (and the Mrs wanted all three to match....which I liked as well for the simplicity of having repair parts on hand that were all the same) The rough-in that was 11" used the standard 12" adapter....the plumber tried a ten but the toilet sat too far from the wall. One bathroom had a 12" rough in so that went smooth. The final one was roughed in at 9 1/2 and even with the ten inch adapter the baseboard still had to be notched a tad.

Anyway, all three function great. My plumber wished all of his installs went as smoothly and repeatedly commented on the quality of the parts. Although two of my supply line inlets were closer in than Toto's spec sheet called for, that worked out well too.

Mort

abak_soiree_1.jpg

TOTO Soiree pedestal lav, faucet and toilet suite
 
Last edited by a moderator:

x77dude

New Member
Messages
4
Reaction score
0
Points
0
Location
Santa Clara, CA
Apparently, Kohler uses different "guts" for its Class 5 toilets. I have installed a pair that have the same flush valve as in the photo... but the most recent ones have a large diameter cylinder that lifts up when you trip the lever to allow the water to flow into the bowl. The only issue that I have had with mine of that style is that the hose from the ballcock valve sometimes comes loose and won't allow the flush valve to seat properly. Other than that, it works perfectly.

I actually LIKE the "defect" posted by Dfhsah-- a quick trip of the lever gives a minimal flush that's very appropriate for liquid waste. If I've "dumped a load" in the bowl, I just hold down the flush lever. It's like a "dual flush" model without the complexity of a dual flush system. Win-win IMHO. YMMV.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
None of the modern toilets empty the tank with a normal flush. Holding the lever down will end up using as much as twice the amount it is supposed to. If you need that to flush, it is NOT a good toilet. Any modern toilet does what you are talking about. Only an engineered one designed for dual flush does it well.
 

Charlie 3

New Member
Messages
2
Reaction score
0
Points
0
Location
Charleston, WV
Just Fixed My Kohler Flapper - Try This!

The flush handle doesn't have enough travel. I took mine apart, and trimmed back the plastic opening that the handle slot travels in. I used a utility knife. I took a little off each side, making the travel about twice as much. It works like a charm. It probably doesn't meet the EPA requirements, but I don't have to worry about my guests having embarrasing problems.




cimarron_inside_tank.jpg


Just installed my new Kohler Highline Class Five toilet. The flapper valve closes instantly upon release of flush handle not allowing enough water to flush properly. Only a small amount of water returns to bowl. The temporary solution is to hold down the flush handle for approx. 3 seconds to get a good flush.

Have spoken with Kohler and have not been able to resolve the problem.

Has anyone had a similiar problem with the class five flushing system?
 
Last edited by a moderator:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks