| Posted by Terry Love on September 23, 1998 at 20:02:29: | |
| In response to Re: what is a wet vent ? | |
I don't understand it either. I am from Washington State, which uses the UPC plumbing code. I don't know which code is used your state. As you see below, the UPC code requires that any wet vent takes place on the "same" story. UPC code 97 edition 908.2 The vertical piping between any two (2) consecutive inlet levels shall be considered a wet vented section Each wet vented section shall be a minimum waste pipe size of the upper fixture or shall be one (1) pipe size larger than the required minimum pipe size for the sum of the fixture units served by such wet vented section, whichever is larger, but in no case less than two (2) inches. |
| There are none. |