Which Pressure switch to use

Jimdandy

New Member
Messages
3
Reaction score
0
Points
0
Location
Pennsylvania
Can I use a FSG2 Square D 40/60 pressure switch with my 1.5 HP GOulds Deep well Pump?
Everything I have read that tells me the rating on that switch says it can be used up to 1 HP? The next one up though is a 3HP switch.
 
What size is your tank, and how deep is your pump set. We use the 40/60 switches predominately, unless the customer requires otherwise. Some people use 30/50 switches, and some like 60/80 heavy duty pressure switches. Why are you trying to match the switch to the pump? Were you told to, or do you have a specific application?
 
The square D FSG2 is rated up to 1.5 HP operated on 115 volt and 2 HP on 230 volt. You don't mention which voltage your operating on but most jet pump motors are dual voltage and are easily changed.
 
Last edited:
Yes you can use it. It will work fine without any problems.
There fine up to about 17amps, any higher than that, and it is better to use a contactor with the switch.
For your pump it will be fine.


Travis
 