Gas hot water heater, problem

tommyo

New Member
Messages
8
Reaction score
0
Points
0
Location
RI
Ok I soldered a leak on the one zone valve, this system has 2 zones , one circulator,(I bled system) I fired the furnace back up, the water heats inside to 200f and pressure is about 17psi , I get no heat through the pipes up or down zone, (I even tried leaving zones manually open). does this mean that the circulator is bad, everything else seems to be working fine, damper, evrything eletric seems good, the thermostats triger the sytem, just no heat, I am really baffled, any help greatly appriciated.:confused:
 
I think you probably have an air lock. Need to bleed the high points.
 
reply

I checked all high points, there are no bleeders anywhere on top floor, it has an automatic air bleeder on top,
 
you might have a slow-operating or non-operating automatic bleeder.
If you can work fast, you might be able to replace it with a manual bleeder, and that may be all you need to do
 
If you have no vents then you must have a loop system and the system needs to be purged. If you can post a picture of your boiler and piping I can walk you through it, or you can call a plumber.

John
 