Zone valve sizing

Users who are viewing this thread

jpiazza

New Member
Messages
18
Reaction score
0
Points
0
Hi to all. I am zoning my Peerless boiler into two zones one feeding the first and second floor with 1 1/4" pipe and the second zone feeding the basement with 1" pipe. Do my zone valves have to match the diameter of the pipe they are serving? Also any advice on which valve would best work with my system would be greatly appreciated. I have a Honeywell L8148E Aquastat and a B&G NRF-22 circulator. Thanks
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
No they do not need to be of the same pipe size. Just capable of flowing the desired GPM to meet radiation requirements for heat loss, at given head, temp & delta T
 