    I have caused my self some headache. I had to dig up my well head to add a pitless adapter that was left out by the installer. In the process some dirt fell into my well. (I found an old license plate cut to block the oversized hole in the side of my well pipe) My pump has sucked some gravel and the system won't hold pressure. I pulled my pump up, it is a 110v sears 40/60, but I can't find the check valve. Is it in the pump, if so is it serviceable?
  2. speedbump

    speedbump Previous member

    Messages:
    4,540
    Location:
    Riverview, Fl.
    Your going to have to send some pictures or give a better description of what you have before I can help.

    bob...
  3. Gary Slusser

    Gary Slusser That's all folks!

    When you say it won't hold pressure, do you mean when the pump shuts off the gauge shows the pressure falling until the pump comes on again? Is that why you question the check valve, do you think it isn't closing?

    You only need a pitless adapter if you are in a freeze area.
  4. akbrent

    akbrent New Member

    Messages:
    3
    thanks for your interest. I live out in the woods in alaska and my dial up internet would take all day to send a picture. If I can't describe it better I will try a picture. The pump is 34 long 3.75 d the motor is on the bottom and the intake is in the middle. The motor bolts are in the intake channel. The casing is stainless. At the top of the pump is a cast cone that necks down to 1" npt, on the side of the cone is a 5/16 bolt. I would assume the check valve has to be above the pump, but the top cone seams crimped on. If there is one in line I can't find it.
  5. akbrent

    akbrent New Member

    Messages:
    3
    Gary, yes the pressure dumps in about 3 sec from 60-40 then back up when the switch kicks in. If I shut off the breaker it will go to zero. I live in alaska, it freezes.
  6. Gary Slusser

    Gary Slusser That's all folks!

    You can buy an inline spring loaded check valve and screw it in/on the pump's outlet if you can't get the internal one off or out. Although if the old one falls just right in its housing it can reduce flow.
Similar Threads: won't hold
Forum Title Date
Pumps and Tanks Well Forum & Blog Won't hold pressure Oct 19, 2012
Pumps and Tanks Well Forum & Blog Pump Won't Prime or hold prime May 30, 2011
Pumps and Tanks Well Forum & Blog Pump won't hold pressure when running water. Mar 3, 2009
Pumps and Tanks Well Forum & Blog won't hold pressure Apr 27, 2008
Pumps and Tanks Well Forum & Blog Won't hold pressure Jun 9, 2007

Share This Page