Wiring for boat lift motor

Discussion in 'Electrical Forum discussion & Blog' started by FlaMike, Feb 12, 2010.

  1. FlaMike

    FlaMike New Member

    Messages:
    2
    Location:
    FL
    Motor is currently serviced by 12ga romex which I do not believe is enuf for the long run out the dock.
    I have a new circuit, 50amp breaker, 8ga stranded copper, to start from the house. We are looking at 700ft from the panel to a 1 hp motor which draws 13.4amps @ 115v. I plan to run wiring in PVC. Questions: do I have to use #8 wires or could I use #10 with a #12 ground? Does stranded vs solid copper make any difference?
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,889
    Location:
    New England
    Some motors can be rewired to run at either 110 or 220vac. If yours can, consider rewiring it for 220. The voltage drop would be less, allowing you to run smaller wires. See what the pros have to add.
  3. Lightwave

    Lightwave New Member

    Messages:
    98
    Location:
    Vancouver, BC
    To be frank, if you have to ask about hooking up #10 to a 50 amp breaker, then you don't have the background to do this job safely. Please call an electrician before you hurt someone.

    When it comes to wiring marine equipment at extreme distances, what you--and most non-pro message board participants, including myself, don't know--can very easily kill you. In addition to the minimum safe wire size for your breaker, you also need cable intended for use below ground (in PVC), you need to deal with the voltage drop issue somewhow, you need to meet requirements for motor overcurrent protection and service disconnects, and you need to address grounding and GFCI issues specific to dock equipment. #8 wire probably won't burn up under fault current held by a 50A breaker, but it won't address any of the other issues.

    Call a pro.

    I suspect the easiest solution may be to use a portable generator.
  4. FlaMike

    FlaMike New Member

    Messages:
    2
    Location:
    FL
    THANKS!.... agree a portable generator is best solution.... saves $$ and many hours in the wetlands and needed one anyway for outages.
  5. codeone

    codeone Code Enforcement

    Messages:
    160
    Location:
    North Carolina
    NM cable nor UF cable are approved for use on at or going to boat docks! Call an electrician!
  6. alfredjoaquin

    alfredjoaquin New Member

    Messages:
    1
    Location:
    UK
    Before repairing it, I think it needs a lot of experience for giving a connections.So i would suggest you to go for a good electrician.
  7. skdaddle

    skdaddle New Member

    Messages:
    4
    Location:
    sc
    It may be possible to get your local power company to install a meter pole closer to your dock, where you could install a panel box with GF breakers for the dock system. 700' is a long way.
  8. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Messages:
    991
    Location:
    NY State, USA
    skdaddle, you do realize this thread is well over a year old......
  9. skdaddle

    skdaddle New Member

    Messages:
    4
    Location:
    sc
    Ha, it sure is! I am also well under a few days new to this site, still have lots to learn about navigating it, thanks!
Similar Threads: Wiring boat
Forum Title Date
Electrical Forum discussion & Blog GFCI wiring Jun 2, 2014
Electrical Forum discussion & Blog Hot Tub Wiring May 28, 2014
Electrical Forum discussion & Blog Questions on old wiring stapled to bottom of joists Apr 16, 2014
Electrical Forum discussion & Blog Wiring and layout for barn Mar 5, 2014
Electrical Forum discussion & Blog Wiring in a 220 circuit for Tankless water heater - Cunduit from behind the wall? Nov 21, 2013

Share This Page