Wire size for Induction Cooktop and seperate double oven.

Users who are viewing this thread

MrBillyd

New Member
Messages
10
Reaction score
0
Points
0
Location
Scottsdale
My house was built in 79. I am removing my 30 year old stove/double oven combo.
The wire that is being fed from the 50amp breaker is about 80 feet long.
The markings say Stabiloy Type SE XHHW 300volts to ground 3CDRS 6 AL
My new situation will be an Induction Cooktop on one breaker and seperate double oven.
The cook top takes a 50amp breaker and the double oven takes a 40amp breaker (per the spec sheets)
I am pulling another feed which will be 6/2

Which wire should I put on my 40amp breaker?
My 30 some year old AL wire has been on the 50amp circuit without issue.
If the 6/2 could handle the load on the Induction cook top better, then I would swap them:)

Bill
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
6 SE AL is only rated for 40A.
Often double ovens are not straight 240V and would need three conductor plus a ground. Are you sure 6/2 will work for the oven?
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
It is probably 6/2 entrance cable which, in the old days, used the outer wrapping for the neutral and ground. Both the oven and cooktop need a 120/240 circuit because of the control wiring. Good call going with induction cooktop. For a long time reasonably priced and available ones were nonexistent. Fortunately, my original one lasted long enough for new 36" models to become available.
 