    This is a question for professional plumbers only, please thanks.

    Suppose a home with an attached garage, and the gas water heater is in a closet in the garage.

    One morning, the resident finds about a half gallon of water on the garage floor, that has seeped out from the bottom of the water heater closet. The hot and cold lines to the water heater disappear in the back wall of the closet. The temp-pressure relief valve is piped into a side wall of the water heater closet, and exits that wall at a point just outside the closet onto a point over a sheet of linoleum next to the water heater closet, and the top of the linoleum seems dry. The interior of the water heater closet seems dry and the exterior of the water heater seems dry. The water heater sits in a pan which seems dry.

    With every water appliance unused for ten minutes, the water meter does not move at all.

    The resident mops up, but every time they check (every 4-6 hours), there is more water.

    The water heater was installed about 18 months ago ( immediately prior to putting the house for sale, which took 9 months during which the house was vacant ).

    As a plumber, how do you proceed ?
  2. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    I would suspect the T&P is discharging from thermal expansion...
  3. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    1 - Do you mean that the T&P is defective ?

    2 - What about the linoleum being dry under the T&P's discharge pipe ?
  4. nhmaster3015

    nhmaster3015 Master Plumber

    Messages:
    836
    Location:
    The granite state
    It's me. I sneak in there about 2:00 am and pour a cup of water on the floor. :)

    Naaaaaaaa. It's probably what Red said. Thermal expansion.
  5. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    You have answered the basic questions, so now it is more a Dick Tracy issue. Someone is almost just going to have to be there to see it happen.

    If you haven't already, get a stong flashlight and some dry tissues, and poke all around the base of the wall of the clost, and all around the overhead area, looking for signs of wet.
  6. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    If it was a leaking pipe it would be a constant leak.
    It's not the water heater cause the pan is dry.
    That pretty much says its the T&P Discharging from thermal expansion.
    The reason the floor appears to be dry under the T&P discharge is probably because the floor directly under it is a high spot.

    Run a good amount of hot water so the water heater starts reheating shut off the water and don't run any water hot or, cold, then go watch the T&P start dripping.

    The T&P if it drips isn't bad it's just doing its job and you need a thermal expansion tank installed.
  7. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    Can a thermal expansion tank be installed in the same place in the system previously occupied by a water softener (which was replaced with a pipe) ?
  8. nhmaster3015

    nhmaster3015 Master Plumber

    Messages:
    836
    Location:
    The granite state
    anywhere on the cold water line
  9. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    In this case, the city water department states that there is no check valve or back-flow preventer in the water meter. So, unless I am not understanding this correctly, then this is an "open system" and so a thermal expansion tank is normally not needed.
  10. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    Do you have a pressure reducing valve?

    [​IMG]
  11. nukeman

    nukeman Nuclear Engineer

    Messages:
    711
    Location:
    VA
    ... or perhaps a check valve leftover from where the water softener was installed?

    It would be a good idea to see what the pressure of the system is doing to see if you may be hitting the setpoint for the T&P.

    Another possibility is that there is a pinhole leak in the pipe after it goes into the wall. May be slow enough to not show up on the meter, but enough to accumulate after a couple hours. Have you checked for soft spots in the drywall?
  12. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    Where would this typically be found in the installation ?

    I do not think there is one in this case.
    Last edited: Aug 3, 2010
  13. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    It depends largely on where you live...
    Some places they might be out side on an underground meter box, Others they might be in a basement or crawlspace with the meter, sometimes in tha garage or, a utility room where the meter is located.

    Generally it is new=ar the meter wherever that is located but, it may not always be...
  14. Cookie

    Cookie .

    Messages:
    5,658
    Location:
    .
    How to eliminate the T&P as a possible source of the problem is to simply place a cup directly under the T&P discharge point and wait to see if it collects water. If it doesn't collect water you have eliminated the T&P as the problem.

    The simplest way is the best way and I am not a plumber. :)
  15. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    I have noticed that you can get a hose-bib pressure gauge for under $10. It seems that a simple test would be to simply hook one to the drain valve, open it and cause the heater to cycle on.
    ...
    Also, while there are certainly correct reasons for the relief valve to release water, isn't it also possible for the relief valve to be defective ?
  16. Cookie

    Cookie .

    Messages:
    5,658
    Location:
    .
    If you open the drain valve on the water heater, you could be causing yourself more problems. You could be causing yourself a steady leak.
  17. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    If it opens and closes by itself it is working usually.

    When they go bad they usually will not open or, will not close.
  18. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    The required regular maintenace on a water heater is turning it off, opening the drain valve and draining the water heater (check your water heater manual for specific instructions.)

    If your drain valve leaks, replace it with a better one from your local hardware store.
  19. Cookie

    Cookie .

    Messages:
    5,658
    Location:
    .
    Unless you have been performing the maintenace from the day the water heater was installed and if you live in a hard water mineral area the build-up in the water heater can lodge itself on the seat/washer & can cause the valve to leak and require replacement.

    ... and that is the truth. :)
    Last edited: Aug 4, 2010
  20. kstuart

    kstuart New Member

    Messages:
    43
    Location:
    Central Coast CA
    So then replace the drain valve for a few dollars at your local hardware store.
Similar Threads: situation
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Unique island vent situation Apr 28, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Stumped on venting situation Apr 14, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Can I offset my stack horizontally in this situation? Mar 28, 2014
Plumbing Forum, Professional & DIY Advice, Tips & New to plumbing. Watch out! What would you do in this situation? Mar 20, 2014
Plumbing Forum, Professional & DIY Advice, Tips & What type of sealing compound to use for this situation Dec 15, 2012

Share This Page