With a 52K output boiler and 56' of baseboard the burn times would be reasonably long, especially since it comes equipped with heat purge control.
But if the other zones are all 20 footers (or shorter) it would still benefit from having more thermal mass to work with.
Seriously, since you have plenty of time, build yourself a spreadsheet, and run your own room by room heat load numbers based on construction, and see if you can't consolidate some zones. For a primer on how that's done,
try this bit o'
bloggery. For purposes of figuring out the ratio of radiation to load high precision is not required. You can just use +10F for the outside design temp, and 70F for the interior design temp (a temperature difference of 60F), and ignore the infiltration losses. If you shared a bit with how your walls are constructed & insulated, the window types (including storm windows), and attic insulation etc, I could cook up reasonable U-factors to use for the calculation. The basic calculation for each exterior surface type is:
U-factor x square feet x temperature difference = BTU/hour.
Add up the square feet of window in the room, run the arithmetic, the total square feet of wall area (subtracting out the windows & doors) , run that arithmetic, the total amount of top floor ceiling, run the numbers, and add it all up. Then divide the room total BTU/hr by the linear feet of baseboard in that room.
For instance, say you have R30 in the attic (a U-factor of about 0.04), and 2x4/R13 walls (U-factor of about U0.10) and wood sash double hungs with clear glass storm windows (about U0.50) . A 10 x 15 corner room with 9' ceilings and three 10 square foot windows has 30 square feet of window, 195 square feet of wall, and 150 square feet of ceiling, and let's say it has 14' of baseboard.
Window losses:
U0.50 x 30' x 60F= 900 BTU/hr
Wall losses:
U0.10 x 195' x 60F= 1170 BTU/hr
Ceiling losses:
U0.04 x 150' x 60F= 360 BTU/hr
Add it all up the total conducted loss comes to: 2430 BTU/hr
Load to baseboard ratio: 2430/14= 174 BTU/hr per foot of baseboard.
If other rooms have similar ratios, with the highest being within 15% of the lowest, they will tend to track OK when zoned together. So if that 174 is the middle number, rooms with ratios between roughly 160 BTU/hr per foot and 190 BTU/hr per foot would work OK operated as a single zone, but a room that came out at 280 BTU/foot-hour would run cold, and a 120 BTU/foot-hour room would run warm if lumped into a zone with a ratio of 175 BTU/ft-hr.
Sometimes it's worth adding or subtracting a bit of radiation from a room to make it work well. Most people prefer the bathrooms to be a bit warmer, and bedrooms a bit cooler, and that can be factored in a bit too.
For a 52,000 BTU/hr output boiler like the Burnham ESC-3 it's worth having at least 50' of baseboard per zone if you can, and more is definitely better. If That's simply not possible otherwise you can go with a Turbomax or something kept at 160-180F and keep the micro-zoning. Unless you have a monster-sized spa to fill, a 28-30 gallon reverse indirect kept at 160F+ with 52K of burner behind it would be good enough for most homes. (I have a 48 gallon Ergomax, which is somewhat marginal on tub-filling hot water performance due to the fact that I'm running it at ~125F, not 180F. But in combination with a drainwater heat exchanger it is enough for effectively endless showering capacity, even with all zones calling for heat.)