Water? in the bottom of furnace/AC cabinet

Users who are viewing this thread

tregg

New Member
Messages
31
Reaction score
0
Points
0
Location
Iowa
I went to change the air filter and noticed an inch of water standing in the bottom just below the squirrel cage fan. I don't see any drain hose at that level so I take it somethin ain't right. I wonder where's it coming from and what to do about it. I guess I'll drill a hole in the side at the bottom but should I call somebody? The air's been running a lot lately with all the heat.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The condensate drain is likely clogged, and instead of running out the drain, is backing up into the cabinet. You need to clean the drain which starts in the tray underneath the evaporator coil (it could be clogged anywhere in that pipe). One time I had a similar situation, and found a woody fungus that clogged it all up, but it's often dust and mold.
 
Messages
951
Reaction score
6
Points
18
Location
Midwest
In a rental I lived in for a long time we had regular problems with pink algae clogging the condensate drain. I used bleach once a month to suppress it until the drain finally clogged solid. The problem at that point was the cast iron standpipe was solid packed (iron scale takes up over 7 times the volume of the original iron if I remember correctly.) Once it was augured out and a large bore PVC pipe inserted I never had to mess with it again (no bleach either.) A few years later I had to clear all of the iron pipes going though the slab and the run to the street main as well. Actually cleared the latter twice as a parachutist went MIA down the commode...ah the joys of pre-schoolers. Didn't have to tie a yellow ribbon on the magnolia, because we recovered the poor wayward soul out in the yard.

Another possibility is that the evaporator is icing up internally and blocking the drain.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Yearly maintainence needs to be done on AC units and clearing the pan drains is part of that along with cleaning the condensor coils
 

tregg

New Member
Messages
31
Reaction score
0
Points
0
Location
Iowa
I think I got it-the installers left no clean out access so I had to drill thru the pvc and when I ran a snake all the goodies came out. thx for the advice
 

TheycallMeDave

New Member
Messages
13
Reaction score
0
Points
0
Location
Northern Florida
The a/c system is likely low on freon which causes the evaporator above the furnace to freeze the condensate on it until it overflows the evaporator condensate pan and starts to drip down the center of the furnace winding up on the floor underneath the blower. Have the a/c system serviced and before the Service Tech comes out, shut off the system so the ice buildup on the evaporator can thaw .
 