    I installed a new Whirlpool 50-Gallon Energy Smart Electric Water Heater EE2H50RD045V myself several months ago. I thought I did a good job installing it. Just my luck, after returning from a short vacation, I had no hot water. I found the circuit breaker had tripped. I noticed a burn hole in the plastic control panel of my water heater. With the power off, I removed the cover to find that one of the wire nuts melted and the wire (fortunately) shorted on the ground wire. About three inches of wire insulation melted away. I installed this unit so I figure I screwed something up. What might have happened?
     

    Attached Files:

  2. Lightwave

    Lightwave New Member

    Joined:
    Aug 20, 2007
    Location:
    Vancouver, BC
    Looks like you had a bad connection in the melted wirenut. The wires may have been loose, oxidized, or nicked. The wirenut may not have been been the wrong size or may have been incorrectly tightened.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    Usually that means a bad connection in the wire nut, so there was added electrical resistance which caused heat and that melted the wire nut and the insulation.
     
  5. cacher_chick

    cacher_chick Test, Don't Guess!

    Joined:
    Jan 5, 2008
    Occupation:
    Test, Don't Guess!
    Location:
    Land of Cheese
    Looks to me like the connection was bad.

    It's hard to tell by the picture but I'm not sure that your incoming wires are the required 10 gauge wire either.
    Should be all 10 gauge wired to a 30A double pole breaker.
     
  6. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    If the factory wires to the panel are #10,which is not usually the case except for 5500 watt elements, which this unit does not have, then it appears that the customer's wires are #12. It would be even worse if the factory wires are #12, because then the connecting wires which appear to be smaller would be #14.
     
Similar Threads: Water Heater
Forum Title Date
Electrical Forum discussion & Blog Tankless water heater ... dedicated to washing machine Jul 11, 2015
Electrical Forum discussion & Blog 120v w 19 gallon water heater run on 2 pole 230v breaker. is it safe? Jul 9, 2015
Electrical Forum discussion & Blog New circuit for gas water heater Dec 7, 2014
Electrical Forum discussion & Blog Removed Electric Hot water Heater - Breaker Filler Plate? Mar 6, 2014
Electrical Forum discussion & Blog Gas water heater bonding Jan 8, 2014

Share This Page