Water Heater Pressure Relief Valve Leaked About a 2 Quarts of Water

Discussion in 'Water Heater Forum, Tanks' started by hudson, Jul 2, 2009.

  1. hudson

    hudson New Member

    Messages:
    15
    Location:
    NC
    My water heater and pressure relieve valve were installed by me in 2000. The tag on the pressure relieve valve says 150 PSI. I'm on a city water system. I don't have any backflow valves or pressure tanks in my system. I test the valve at least once per year. I have a quart jar under the pipe leading from the pressure relief valve. About 2 quarts of very hot water came through the side mounted valve. I operated the valve 5 or 6 times; it has not leaked a drop since then...that has been two hours. The water is definitely coming through the valve and not from around the sides of the valve. I read a number of other threads. We've been using hot water on and off all day for bathing, and washing clothes/dishes. What's my next move?
  2. Redwood

    Redwood Master Plumber

    Messages:
    7,453
    Location:
    Connecticut
    What is your water pressure?

    Do you have a pressure reducing valve installed?

    [​IMG]
  3. Gary Swart

    Gary Swart In the Trades

    Messages:
    7,302
    Location:
    Yakima WA
    The point of Redwood's question is, do you have a pressure regulator valve like the one pictured? If you do, then you should have a thermal expansion tank between the pressure regulator and the water heater. Otherwise, when the water heats, it expands. The pressure regulator prevents the expansion from being absorbed by the city water main so when the pressure reaches the limits of the T/P valve on the tank, it releases the excess pressure. Now, I can not tell you when this has just now begun to happen, usually it is an immediate condition. It is possible the T/P is failing although that is unusual if it's only a couple of years old.
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,809
    Location:
    New England
    Or, if you have an expansion tank, it has failed.
  5. hudson

    hudson New Member

    Messages:
    15
    Location:
    NC
    "What is your water pressure? Do you have a pressure reducing valve installed?" Expansion tank? Age of valve?

    I don't know my water pressure...but I'm willing to get it checked. I think that I read on other threads to buy a device for about $10 and put it on an outside spigot.

    No pressure reducing valve.
    No expansion tank

    Not one drop of water has leaked since I first found the big puddle in the garage. At that time, I worked the valve on the water heater several times.

    The pressure relief valve on the side of the water heater is a year 2000 model...that's 9 years old.

    I called my local utility to find the water pressure...no answer...holiday?
    I'm on my way to get a pressure gauge...I'll check the pressure and post the result.

    Thanks for your assistance!
    Last edited: Jul 3, 2009
  6. SteveW

    SteveW DIY Senior Member

    Messages:
    1,053
    Location:
    Omaha, NE
    Here's another test that would help make the diagnosis. Hook up your new pressure gauge to a hose bib (for example, your cold water source for your washing machine) and see what the pressure is. Then, run some hot water by turning on a tub faucet to full hot and let it run for 5-10 minutes. Then shut it off, make sure no one in the house runs any water and watch the gauge.

    If you have thermal expansion going on, your pressure will rise during this period - possibly dramatically.
  7. hudson

    hudson New Member

    Messages:
    15
    Location:
    NC
    The water pressure was 25 psi.

    When I went to hook up the pressure tester, I had to remove a garden hose. The spigot was on, a valve at the other end of the hose was closed. The hose was in the sun. The temperature was over 90 degrees yesterday. The hose in the back yard was the the same...spigot on...valve at the other end of the hose closed. Two garden hoses...both in the summer sun...both spigots on...would that increase pressure in the system?

    again...no leaks or problems since yesterday.
    Last edited: Jul 3, 2009
  8. SteveW

    SteveW DIY Senior Member

    Messages:
    1,053
    Location:
    Omaha, NE
    25 PSI is pretty low.

    I doubt that the thermal expansion you would get from hoses in the sun would be enough to cause house PSI to exceed 150 PSI. Also, the hose would burst before that.

    I'd still opt to take 10 minutes and do the test I mentioned.
  9. Ladiesman271

    Ladiesman271 Homeowner

    Messages:
    221


    My temperature / pressure relief valve went bad after about a year of use. The temperature part of the valve went bad. I changed it and all is well. They only cost around $15, so buy a new one and change it out.

    My normal water pressure is around the 60 PSI area.
Similar Threads: Water Heater
Forum Title Date
Water Heater Forum, Tanks Noob question about hot water heater Jul 13, 2014
Water Heater Forum, Tanks Water heater size with and without tempering valve Jul 12, 2014
Water Heater Forum, Tanks Venting options for gas water heater Jul 6, 2014
Water Heater Forum, Tanks Water Heater drain valve failure Jun 26, 2014
Water Heater Forum, Tanks water heater over temp (T & P ) valve piping question Jun 25, 2014

Share This Page