Water Heater Inspection - Drain Valve Angle Question

Discussion in 'Water Heater Forum, Tanks' started by luckycharmz336, Jul 23, 2010.

  1. luckycharmz336

    luckycharmz336 New Member

    Joined:
    Jul 23, 2010
    Location:
    AZ
    The water heater drain valve angles about 2 inches up hill from the water heater to the wall, the inspector said this is an issue and safety hazard. How concerned should we be able this? Below is a picture [​IMG]

    We want to have it fixed if it is a major issue, however, if we shouldn't be concerned I don't want to force them to change it. Thanks
     
  2. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    Cut the wall and lower the 90 in the wall.

    Below is my favorite exploding water heater video.
    In the Seattle area, a water heater shot though a garage roof and landed blocks away.


    [video=youtube;GF_Wrm-Ns0I]http://www.youtube.com/watch?v=GF_Wrm-Ns0I[/video]
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. 3m

    3m New Member

    Joined:
    Mar 3, 2009
    Location:
    NY
    where is the line going to
     
  5. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego
    It is a fairly serious problem. Almost guaranteed that as time goes by, some drippage will occur from the valve, or some condensation will occur in the line. This water will sit right there at the relief and leave mineral deposits, clogging the valve. It might not work when it needs to.

    Somewhat shocking that it is done this way.....obviously no permit because the inspector would still be looking for a big enough crayon to write NO WAY.....all over the papers!
     
  6. Redwood

    Redwood Master Plumber

    Joined:
    Dec 15, 2007
    Occupation:
    Service Plumber
    Location:
    Connecticut
    It is a definite FAIL...

    It will cause the reliability of the T&P valve to suffer and could result in a hazardous condition....
     
  7. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    The easiest way to correct it is to place some concrete blocks, or a few circular concrete stepstones, under the heater to raise the valve above the opening in the wall. That corrugated connector is also "illegal" in most areas. Use copper tubing to connect the SAFETY valve, (not a DRAIN valve), to the pipe at the wall. In Phoenix, the heater landed a block away, and the house had to be demolished because it was not repairable.
     
    Last edited: Jul 24, 2010
  8. Redwood

    Redwood Master Plumber

    Joined:
    Dec 15, 2007
    Occupation:
    Service Plumber
    Location:
    Connecticut
    Sorry to see that you have a Whirlpool Energy Smart water heater as well....
     
Similar Threads: Water Heater
Forum Title Date
Water Heater Forum, Tanks Water heater keeps starting then stopping Friday at 7:28 AM
Water Heater Forum, Tanks Trying to get verification on water heater wire size Tuesday at 3:14 PM
Water Heater Forum, Tanks Whirlpool water heater date Aug 22, 2015
Water Heater Forum, Tanks Blocks under gas water heater Aug 16, 2015
Water Heater Forum, Tanks Hot water heater help! Aug 15, 2015