Water Heater Gas Supply Question
Discussion in 'Water Heater Forum, Tanks' started by molo, Mar 3, 2010.
  1. molo
    molo Member
    Sep 23, 2006
    Cold New York
    Hi,
    I'm hoping somebody can tell me the required size natural gas supply line for a 120,000 BTU Boiler and a 40,000 BTU Hot water tank. I'm not certain of the supply pressure, but it is less than a pound. This will be black iron pipe.
    Thanks for any replies!
  2. jimbo
    jimbo Plumber
    Starting AT THE METER ..3/4" pipe would carry 160,000 BTU not over about 20 feet. 1" pipe would carry it 75 feet or so. If you tee off somewhere, you have to factor in the total BTU load on any leg of the pipe run.
  4. hj
    Gas pipe calculations are based on the TOTAL length of the piping to the furthest appliance. Then each section of piping is sized according to the total BTU's of the appliances up to that point. Natural gas is either low pressure, i.e. 6-8 iwc, or medium pressure, 2 psi, and the sizing tables reflect the differences.
  5. molo
    molo Member
    Sep 23, 2006
    Cold New York
    The pressure is approx 7-9 iwc. The water heater (40,000 btu) is right next to the boiler (120,000) and they are about 25 feet from the meter. There is a leg for a gas oven/range that is 15 feet to the side. Here's a rough sketch.
    25 feet
    meter--------------------------------------------------------------water heater and boiler
    gas oven/stove
    15 feet to the side
Similar Threads: Water Heater
Water Heater Forum, Tanks Adding heat pump water heater alongside ancient boiler coil Wednesday at 10:49 AM
Water Heater Forum, Tanks Help picking electric water heater Feb 11, 2017
Water Heater Forum, Tanks Water Heater Leaking from the bottom. Feb 5, 2017
Water Heater Forum, Tanks Water Heater Choices Feb 5, 2017
Water Heater Forum, Tanks Richmond Water heater code 6 problem Feb 3, 2017