    2009 International Plumbing Code P3109.1 Waste Stack Vent Permitted

    The stack shall not receive the discharge of water closets or urinals.

    What does this mean?

    I thought the waste stack discharged all waste
  2. jc60618

    jc60618 DIY Junior Member

    Messages:
    88
    Location:
    Chicago
    Water closets and urinals must drain into soil stacks.
  3. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,245
    Location:
    Cave Creek, Arizona
    The statement says it is referring to a "waste stack vent", and a vent stack SHALL not have toilets or urinals connected to it, but you can use it to wet vent by connecting a sink to the vent. However, I HAVE connected urinals to toilet vents when the two are back to back.
  4. ptomt77

    ptomt77 Designer

    Messages:
    4
    Location:
    Easton,PA
    Thank you very much