Voltage at elements & other questions
Discussion in 'Water Heater Forum, Tanks' started by JohnEdgewater, Jan 31, 2012.
  1. JohnEdgewater
    JohnEdgewater New Member
    Jan 31, 2012
    Florida
    I installed new heating elements in my 12yo AO Smith 40 gal. water heater today. I got the elements at Home D. The elements I removed were: top, 3500w 208v shorter; bottom, 4500w 240v, longer. The new elements were both the same length and both 4500w, 240v.
    Quest. 1: Is it okay that I installed 2 of the same type elements?
    Quest 2: Is it okay that the new element I installed in the top differs in watts and voltage than the element removed?
    Quest 3: When I put a multimeter on the two screws that connect the power wires to the element in the top, the meter registers 240v. When I touch the probes of the meter to the screws on the bottom element, nothing. If I touch the meter probes to one of the screws connecting power to the bottom element and touch the other probe to the tank, I get 115v reading on the meter. Is everything okay here? Why no 240 at the screws on the bottom element? Why no reading at all at the bottom element when I touch the probes to both screws?
    Quest. 4: do I need to do anything to the expansion tank on top after I've drained and refilled the water from the water heater tank?
    Thx in advance for any help
  2. jimbo
    jimbo Plumber
    San Diego, CA
    1. Your old elements were the same watts. A given element, which would be approx. 12.5 ohms, would produce 3800 watts on 208 volts, and 4500 watts on 240 volts. Many water heaters are rated at 3800/4500, and that is the deal.
    2. NEVER trouble shoot a water heater by measuring from one terminal to ground.....that will lead you on a wild goose chase every time. The only measurement that matters is directly across the two terminals of the element. Either it has 240 or zero. Note that on a residential water heater, the two elements are never energized at the same time. That would pop the breaker, and the thermostats prevent that from happening.
  4. JerryR
    JerryR Member
    Jul 27, 2011
    Florida
    Answer to quest 3:
    Your readings are normal for a tank that is heating up.
    One terminal on each element will always have 120 vac as measured to ground.
    Upper element runs first. (240vac across both screws)
    Once the top of the tank is hot the upper thermostat redirects one leg to the lower thermostat. If the lower portion of the tank is not up to temp at that time the lower themostat will connect the second leg to the lower element snd you should read ~240vac across both terminals on the lower element.
    Once the tank is completely at temp you will read 0 across the 2 terminals on either element and you still should read 120 vac from one terminal to ground on either element.
    FYI, One terminal on each element always has one of the 120 vac legs connected at all times. The thermostats switch the other 120 v leg as needed
    Jerry
  5. ballvalve
    Dec 28, 2009
    northfork, california
    I get a whole range of readings depending on how the element blew. Some keep running at a reduced rate.
  6. jadnashua
    The implication was 'when operating correctly', not when there was a fault.
Similar Threads: Voltage elements
Water Heater Forum, Tanks GE water heater controller voltage Sep 14, 2013
Water Heater Forum, Tanks IN floor (concrete) radiant heat low voltage pumps Jan 21, 2010
Water Heater Forum, Tanks Rheem Performance 30 gal. Short 6 Year 4500/4500-Watt Elements Electric Water Heater Jun 13, 2014
Water Heater Forum, Tanks 4500w vs 5500w elements Oct 24, 2013
Water Heater Forum, Tanks hot water heater elements Jan 30, 2013