Venting line above window

Users who are viewing this thread

MIKE007

New Member
Messages
19
Reaction score
0
Points
1
Location
Montreal
For some strange reason I have a venting line above a window in my basement. There is a 1" 1/2 vent on the left side and 2" on the right side that connects above the window and goes up above the roof. May I use a double 1/4 bend upside down for this? The space is tight for a sanitary T + 90 elbow.


Thanks,

M.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
The vent must be installed in such a way that allows rainwater and condensation to flow to the drain. There must be pitch to any horizontal run, and there cannot be any configuration of pipe or fittings that will retain liquid.
 