Venting basement DWV system

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by FatsoPilot, Aug 3, 2012.

  1. FatsoPilot

    FatsoPilot New Member

    Messages:
    18
    Location:
    WA State
    I'm trying to figure out how to vent my basement bath and shower drains. In WA state code says you can't roll a vent more than 45 degrees until 6 inches above the flood line of the highest fixture? If I have a drain in the basement along an outside wall that I'm running straight down the middle of the bathroom (so there is no access to a wall to run a vent in any other place in the required distance) and I'm trying to vent along the wall back around the room to the vent, what kind of fittings would I use? Without running the line a few feet close to horizontal I'm not sure how it is physically possible. This is a mock up (a poor one), the wall the line crosses over is too far to meet code so I have to vent out the back. The drain for the bath is going to be a few feet from the wall at the bottom and the other drain is going to be a few feet from the wall on the left.

    Jay's Bathroom211.jpg

    Thanks in advance for any advice (or even better a picture).
  2. Terry

    Terry Administrator Staff Member

    Messages:
    14,943
    Location:
    Bothell, Washington
    For starters, when the tub drains, unless there is a vent for both the shower and the tub, that are separate, the p-trap on the shower is going to siphon dry when the tub drains.

    Washington State UPC
    You can run a 2" trap arm 60" before the vent
    and for a 1.5" trap arm, 42" before the vent.
    The revents need to be 42" above the floor.
    In this case, the shower and the tub have vents that can be tied in together at 42" above the floor.
  3. FatsoPilot

    FatsoPilot New Member

    Messages:
    18
    Location:
    WA State
    Thank you for reply. I was planning on venting them separately and tying them together eventually at least 42" above the floor. Is it possible to vent the tub on the back wall? And the shower on the left wall? If so, how is it possible without running the vent horizontal a short distance? What fittings would allow this to happen or how can I run the lines so I can stay in code when rolling the vent?

    Cheers.
  4. Terry

    Terry Administrator Staff Member

    Messages:
    14,943
    Location:
    Bothell, Washington
    Rolling would be wyes and 45's
Similar Threads: Venting basement
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Venting ejector pit to basement bathroom vent? Mar 26, 2014
Plumbing Forum, Professional & DIY Advice, Tips & basement bath drain/ venting layout Jun 7, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Wet venting WC thru lav in new basement 1/2 bath Feb 23, 2013
Plumbing Forum, Professional & DIY Advice, Tips & basement bathroom venting and plumbing Jan 18, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Venting through exterior wall for basement bathroom? Sep 16, 2012

Share This Page