Vent termination: above roof -vs- out the wall

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by Carradine, Feb 8, 2009.

  1. Carradine

    Carradine Architect

    Messages:
    3
    Location:
    California
    We're working on a house with cathedral ceilings and a metal roof that we do not want to penetrate with vents. California Plumbing Code applies which is based on the UPC. We would prefer air admittance valves (AAV) for secondary fixtures, but they are not allowed. Contrary to our inspector's statement (an ex-plumber for 30+ years), we believe the vent does not need to go "through" the roof, but can go out the wall, see diagram.

    [​IMG]

    Here is the code, CPC sect. 906.1, Each vent pipe or stack shall extend through its flashing and shall terminate vertically not less than six (6) inches above the roof nor less than one (1) foot from any vertical surface.

    And CPC sect. 906.2, Each vent shall terminate not less than ten (10) feet from, or at least three (3) feet above, any openable window, door, opening, air intake, or vent shaft, nor less than three (3) feet in every direction from any lot line, alley and street excepted.

    Since the is no specific requirement to go "through" the roof, all 3 of the vent solutions meet the literal requirements of the CPC. Are we correct, or we the first ones to challenge the ingrained conventional wisdom?

    Thanks for any constructive comments, --MC
  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Nope, you can go out through the side if you keep the clearances proper. No problem.
  3. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Messages:
    885
    Location:
    South of Boston, MA
    Just wondering, Is that diagram from the code book?
Similar Threads: Vent termination
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & 1 final vent termination size? Jun 20, 2011
Plumbing Forum, Professional & DIY Advice, Tips & concentric vent/air termination install questions Nov 25, 2010
Plumbing Forum, Professional & DIY Advice, Tips & Vent pipe termination distance over roof? May 12, 2009
Plumbing Forum, Professional & DIY Advice, Tips & dryer vent termination Feb 29, 2008
Plumbing Forum, Professional & DIY Advice, Tips & Gable vent for DWV vent termination? Jan 16, 2008

Share This Page