vent stovehood into furnace exhaust

Discussion in 'HVAC Heating & Cooling' started by trcmag, Oct 14, 2010.

  1. trcmag

    trcmag New Member

    Messages:
    1
    Location:
    Michigan
    my furnace and water heater vents through the roof and I need to add a exhaust for my stove top. I was wondering if I could avoid cutting a new hole in my roof and put a T in the furnace exhaust pipe and vent my stovetop through this pipe.

    The furnace and water heater are in the basement and the T would be in the ceiling in a single story house in Michigan.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,153
    Location:
    New England
    Not a good idea! You could get CO back into the house, and any grease that made it past the hood's filters, might line the furnace flue and create a grease fire. Don't think code would allow it, either. Often, people vent the range out the side, rather than the roof.
  3. Dana

    Dana In the trades

    Messages:
    2,924
    Location:
    01609
    What jadnashua said- it's (rightfull) a code-disaster, and a real hazard. If the hood vent is power vented, and the furnace/water heater are atmospheric drafted (likely, if they're sharing a flue) you're guaranteed to be driving copious amounts of exhaust into the basement. Side vent it if you can, but use a decent backflow preventer no matter which way you go with it (roof or side.)
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,153
    Location:
    New England
    You really want the vent to be as short as possible. The grease filters generally work fairly well, but the warmer the air is, the more the smoke and grease can stay in suspension. Also, smoke particles tend to stick to surfaces, so the fewer elbows you have, the cleaner the vents will stay. The longer things are, the colder things get, and then you start to have problems. A grease fire in the wall is no fun! NEVER run the thing without the filters in place, and if they get replaced, make sure they are the proper ones. Clean them periodically, too!
Similar Threads: vent stovehood
Forum Title Date
HVAC Heating & Cooling Roof Venting Condensing Gas Furnace Tuesday at 4:23 PM
HVAC Heating & Cooling How illegal is this? Vented gas fixtures Sep 17, 2014
HVAC Heating & Cooling Pieces/parts for Utility room combustion air vents Sep 3, 2014
HVAC Heating & Cooling A/C Condensaye drain P-Trap venting problem Jun 13, 2014
HVAC Heating & Cooling Shared exhaust vents Apr 13, 2014

Share This Page