Vent sizing

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by chuck b, Sep 6, 2012.

  1. chuck b

    chuck b sea-bee

    Messages:
    78
    Location:
    levering, michigan
    Doing DWV for 800' square foot cottage with a septic system. Need to know if 2" vents will be acceptable (with 3" PVC PIPE 1' below and above roof line) for the following:

    Full Bath: Toilet, Sink and Tub/Shower
    Laundry: Drain
    Kitchen: Sink (w/disposal and dishwasher)

    Would prefer to use only 2" if possible for venting. Is a 3" "main line vent" required (Michigan)?


    Thanks
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,261
    Location:
    New England
    Don't know, it's a matter of two things: first, adding up the fixture units, and then, often, at least for the roof penetration, it often needs to be bigger to prevent hoar frost from closing it off in the wintertime. So, you may get by with 2" until it goes through the roof then bumping it up to 3" or even larger. Your local codes will determine this.
  3. Tom Sawyer

    Tom Sawyer In the Trades

    Messages:
    3,261
    Location:
    Maine
    Michigan is IPC so you do not need to run a full size vent through the roof. There needs to be at least 1 vent that is 1/2 the diameter of the building drain which if your main is 4" then you need a 2" vent. All the other individual vents can tie into that one before it exits the roof. The stack size has to be increased to 3" starting 18" below the roof line and extend at least 18" above the roof line to prevent frost closure.
  4. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,019
    Location:
    Cave Creek, Arizona
    THis is a code issue. Some require a "full size" vent from the incoming sewer to the roof, others require that the total AREA, not diameters, of the roof vents must equal the area of the house sewer outside the building. Your area could have a different requirement so you have to contact your building department, not us.
Similar Threads: Vent sizing
Forum Title Date
Plumbing Forum, Professional & DIY Advice vent sizing Jan 16, 2010
Plumbing Forum, Professional & DIY Advice layout for toilet/floor-drain/sink & sizing vent Dec 16, 2009
Plumbing Forum, Professional & DIY Advice basement toilet vent sizing - WI Feb 3, 2009
Plumbing Forum, Professional & DIY Advice Vent sizing? Jan 10, 2008
Plumbing Forum, Professional & DIY Advice Sizing for Washing Machine Vent Jun 14, 2007

Share This Page