    Location:
    Palmer, Massachusetts
    What is the smallest size of vent pipe that can be used to go up from the stack and through the roof? Total load is one toilet, 1 lav sink, 1 shower, 1 kitchen sink. I live in MA if that matters.

    thanks,
     
  2. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    You can vent the entire bath group with an 1 1/2" pipe but..... you need to go through the roof with 3" minimum
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    IT is a local code question, but in many cases a toilet needs a 2" minimum vent, and the TOTAL area, NOT diameters, of the vents out the roof has to equal the AREA of the incoming sewer.
     
  5. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    IPC states that the plumbing sytem must have a minimum of one vent through the roof that is 1/2 the size of the building drain which in most cases would be 4" for residential service so... there must be at least one 2" vent through the roof. However in colder climates state and local ammendments will require the vent to be increased to a minimum of 3" where it makes the roof penetration and perhaps 4" in some places. In my state we have to increase to 3" and that 3" must extend 18" below the roof line and at least 12" above.
     
Similar Threads: Vent size
Forum Title Date
IPC Plumbing Code Questions 2" Vent for Entire Home? Today at 3:25 AM
IPC Plumbing Code Questions 1 toilet - 2 vents? Yesterday at 9:03 PM
IPC Plumbing Code Questions Basement sink vent Monday at 8:07 PM
IPC Plumbing Code Questions Wet venting "by the code" Jul 8, 2014
IPC Plumbing Code Questions double bathroom sinks and washing machine through 2 inch drain - no vent - okay? Sep 11, 2013

Share This Page