Vaillant boiler leaks from Pressure relief valve

Discussion in 'Boiler Forum' started by massangler, Nov 29, 2012.

  1. massangler

    massangler New Member

    Messages:
    1
    Location:
    Newbury MA
    I replaced pressure relief valve, and it still leaks. Boiler cycle hi temp shutoff at 200. As it reaches 200, burner shuts off, but temp and pressure continue to rise afterwards. What settings should I use on honeywell controller? It has high, low and diff. dials
  2. Dana

    Dana In the trades

    Messages:
    2,784
    Location:
    01609
    In general you get better efficiency out of it if you set the low-temp down to 140F (for oil burners), or 130F (for gas or propane), with the biggest possible differential hysteresis. Very few hydronic heating systems actually need a 200F boiler temp EVER, so dial that back to ~180F first, see if that fixes the temperature overshoot. If the aquastat is mis-sensing the temp or has a delay and the thing is overshooting, you may need to re-set the element in the sensor well. If the pressure is going off the charts you may need to re-charge or replace the expansion tank on the system.


    Whether turning down the water temp will work for you from a heating-the-house point of view depends a bit on how much heat emitter/radiation you have. If this is a boiler worth keeping (less than 15 years old, and in decent shape), replacing/hacking around some of the aquastat controls with a smart economizer, it'll do the hysteresis and high temp adjustments automatically. optimizing the system for the actual heat loads. (eg Intellicon 3250 or Beckett Heat Manager, etc.) These typically let you program the low-limit temp, and takes over from there, squeezing out best efficiency it can muster with the system configuration that it can. It won't fix system design issues or oversized boilers, but double-digit percentage reductions in fuel use are common. And the average operating temp (and standby losses) will be much lower.
  3. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,804
    Location:
    New England
    To open, most pressure relief valves need 30# of pressure in the system. Since most domesic systems run about 1/2 of that, something's wrong. First, what is the 'normal' pressure? Then, check your expansion tank. It's probably shot and needs replacement. The, once you get things running as they had been, you can start to tweak the system to make it run better. If you have an autofill, it could be bad. If you have an indirect WH, there could be a leak and potable water is pressurizing the system. Other than that, can't think of any reason other than a bad relief valve that it would open up. The key is to check your pressures first.
Similar Threads: Vaillant boiler
Forum Title Date
Boiler Forum Oil Boiler Problem Yesterday at 6:59 AM
Boiler Forum diaphram expansion tank location on american standard ng boiler Jun 15, 2014
Boiler Forum Could use some help figuring something out. Boiler Jun 14, 2014
Boiler Forum About the National board of boilers and Pressure vessel inspectors May 21, 2014
Boiler Forum My first boiler maintenance, what should I make sure is done? May 6, 2014

Share This Page