Vacuum breaker on deck mount hand held shower

Users who are viewing this thread

Mrikert

New Member
Messages
5
Reaction score
0
Points
0
We were told by the inspector that we needed a vacuum breaker/ anti backflow device on our hand held shower head. I don't understand how to retro-fit such a valve into the system. There was some mention of something needing to be 6" above the deck, not easy to do, with porcelain tiles. Yes it's my mistake, as I didn't know that it was needed.

The fixture is an american standard amaryllis set up

any help would be much appreciated.

Is there such a thing as a replacement hand-held device with an anti siphon valve built into it?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
There are vacuum breaker units which just attach to the hose in series with the shower head. Hopefully, this will be ok for the inspector,.
 

Mrikert

New Member
Messages
5
Reaction score
0
Points
0
thanks for responding...

I tried one of the in-line breakers from Alson, but as soon as I turned on the shower head the water poured through where it met the hose, rather than the shower head... I know that sounds as if it was installed backwards, but it would require a female/ male adapter on both ends to get it to go the other way....

The inspector said that the backflow valve had to be 6" above the outflow.

what's the normal installation for a deck set-up? I can't even find it in my code book.

thanks for any help you can give

Margie
 

Mrikert

New Member
Messages
5
Reaction score
0
Points
0
Resolution of the problem

It turns out that there are hand held shower heads, which have a double check valve within them, and that satisfies the need for a vacuum breaker. American Standard does not, even though their customer service people insist they do, Kohler does.

The inspector who "flunked" us, was satisfied with the Kohler hand held.

Moral of the story, check with local code to see if the anti back flow protection is required, and then either purchase a fixture which has a double check valve in the hand held OR plumb the vacuum breaker into the system (it has to be 6" above the tub overflow)
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Many times the inspector can be very helpful when asked what you need to do to pass.
 

SRdenny

Plumbing Contractor
Messages
359
Reaction score
0
Points
0
Location
SF Peninsula
If I had my way, I'd require manufacturers to build backflow protection into their diverters. Some already do, many don't. There are also wall mount vacuum breakers on the market, but they require forethought on the part of the installer. The problem you experienced is just one of those which crop up when HO's (or GC's, for that matter) buy the fixtures and faucets. Caveat emptor.
 