two zone circulator electrical connections taco to becket afg

Users who are viewing this thread

d trois

New Member
Messages
4
Reaction score
0
Points
0
Location
Boston, MA
:(would attaching the two taco's to c1 and c2 on the aquastat and the two thermostat wires to the tt work. Or do i need to use a taco relay board with 2 or 3 zones? Anyone know?:confused:
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
sure it will work. when you turn either thermostat up, both circulators will run. I assume though that that is not your intent so, yes you will need another relay to call the 2nd zone. You can go with a Taco relay or a honeywell 89a or 854 or one of the newer electronci versions. Either way you need to isolate the thermostats and circulators from each other. Wiring diagrams can be found at www.taco-hvac.com
 