    Can I vent a toilet into an existing vent stack that is 2 inches in diameter and currently only vents a sink? From the toilet trap to the where the vent starts to rise is less then 2 horizontal feet. The vent rises for 8feet then runs on a min 1/4 inch/per ft slope for 4 feet to a tee where it will tie in to the vent stack. Is this acceptable?? Thank You.

    I am in the norhteast.

    ...I posted this in the remodel forum but my post there was not clear.

    Attached Files:

  2. Terry

    Terry Administrator Staff Member

    Messages:
    14,890
    Location:
    Bothell, Washington
    The 2" vent, connected in the ceiling will be fine.
  3. Cass

    Cass Plumber

    Messages:
    5,980
    Location:
    Ohio
    Looks good but use Ys to connect to the 3".....not Ts