Speedy Petey said:
Problem is some folks know just enough to be dangerous.
They know how to figure out the amperage; 4500w÷240v= 18.75A.
Cool, 20a circuit...... right?
WRONG! They don't know the codes regarding things like this.
Math is one thing, codes are another.
To help explain what Petey has posted;
210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served.
Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load
plus 125 percent of the continuous load.
422.13 Storage-Type Water Heaters.
A fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall be considered a continuous load.
Here are two code articles that apply to water heaters. 210.19 states that all continuous loads must have a factor of 125%
422.13 states that a water heater is a continuous load.
Doing the math based on the size of the element in the water heater;
4500w÷240v= 18.75A. we are now required to add another 25% to the load or
18.75A times 125% which would equal 23.43 amps.
Using Nonmetallic cable the requirement in 334.80 that the 60 degree column be used to size the conductors we would be required to use a #10 conductor.
The overcurrent device would be code compliant if a 25 amp breaker was installed.
The use of 30 amp breakers on water heaters has become common place due to an allowance found in 422.11(E);
(E) Single Non–motor-Operated Appliance. If the branch circuit supplies a single non–motor-operated appliance, the rating of overcurrent protection shall:
(1) Not exceed that marked on the appliance.
(2) Not exceed 20 amperes if the overcurrent protection rating is not marked and the appliance is rated 13.3 amperes or less; or
(3) Not exceed 150 percent of the appliance rated current if the overcurrent protection rating is not marked and the appliance is rated over 13.3 amperes. Where 150 percent of the appliance rating does not correspond to a standard overcurrent device ampere rating, the next higher standard rating shall be permitted.
I have a 40 gallon water heater in my basement that has been on a 20 amp breaker with #10 NM cable for a little over two years and used daily that has not tripped.