The House That Didn't Burn Down

Discussion in 'Electrical Forum discussion & Blog' started by Verdeboy, Sep 23, 2007.

  1. Verdeboy

    Verdeboy In the Trades

    Joined:
    Jun 12, 2006
    This customer I'm doing the electrical work for mentioned that one of his exterior lights didn't work, and hadn't worked for months. After ruling out a bad bulb, socket, or lightswitch, I determined that power was making it to the lightswitch and out of the lightswitch, but no power was making it to the light fixture.

    Damn. Time to tear into the walls and look for where the mouse chewed through the Romex. Once the wires were exposed, it was easy to find where the staple had been pounded through the cable, cuz the wire was fused to it, and the 2x4 stud was all burned and charred around it. They must not have been at home when all the arcing occurred, because they never smelled anything burning. Lucky for them, the house didn't burn down. Oh yeah, and the breaker never tripped either.

    Since the breaker didn't trip, my question is: What kind of bad scenarios will trip a breaker and what kind of scenarios (like this one) will not?
     
    Last edited: Sep 23, 2007
  2. Wet_Boots

    Wet_Boots Sprinkler Guy

    Joined:
    Mar 23, 2007
    Location:
    Metro NYC
    There are some new standards for breakers that are specifically designed to detect arcing.

    Reminds me of a college lecture for freshman electrical engineering students given by a professor who was also a volunteer fireman, who posed a question about a burnt-up fusebox in a barn. High resistance in the old screw-in fuse receptacle led to arcing and heat buildup, with a fire coming next on the menu. Useful instruction that was, since some months later, a soft buzzing noise in the basement of a rented house led me to a water-heater fuse-and-switch that was arcing and getting kind of warm.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. BrianJohn

    BrianJohn DIY Senior Member

    Joined:
    Jun 22, 2007
    Location:
    VA
    With a standard molded case circuit breaker (MCCB).

    1. Defective MCCB.
    2. High resistance ground that did not permit current for an instantaneous*1 trip and/or a long time*2 trip before the conductors Burnt free, fortunately.

    I would lean towards a defective MCCB as there should have been a neutral to ground short at some point, but high resistance shorts can result in arcing with out generating sufficient current to trip.

    *1 Instantaneous trip should be in the 6-10 times the MCCB rating, for a 20 amp MCCB this would be 120-200 amps.

    *2 Long time trip should be 30-60 seconds at 300% or at 60 amps the MCCB should operate in 30-60 seconds.
     
Similar Threads: House Didn't
Forum Title Date
Electrical Forum discussion & Blog Advice on feeding house panel from pole mounted meter 200a Aug 28, 2016
Electrical Forum discussion & Blog Is it possible for an amateur to rewire a whole house? Jul 12, 2016
Electrical Forum discussion & Blog Wiring to be done at my house Dec 30, 2015
Electrical Forum discussion & Blog Updating Kitchen wiring in a 60 year old house Jul 10, 2015
Electrical Forum discussion & Blog 20 amp or 15 amp for common household receptacle use? Dec 6, 2014

Share This Page