tapping a steam boiler?

Discussion in 'Boiler Forum' started by dsorkin, Jun 2, 2010.

  1. dsorkin

    dsorkin New Member

    Joined:
    Jun 2, 2010
    Location:
    New Jersey
    Hi,
    I have an old steam boiler that I want to install an electronic Low Water Cut Off into. Unfortunately there is no opening in the side of the boiler where the probe can go. The probe requires a 3/4" NPT tap which would require a 29/32" hole. I imagine I can carefully drill the hole in the side of one of the sections and then cut the threads. What type of drill bit should be used to do this? I know I would use cutting oil to keep it from building up heat while drilling. Should it be drilled in increments of increasing size? Not sure if this is a terrible idea or if there are alternatives to get my LWCO installed with some kind of remote setup.

    The boiler is a 120,000 BTU natural gas Sears / Dunkirk that I believe was manufactured in 1979. Serial Number 7911104.

    Suggestions appreciated.

    Thanks!
    David Sorkin
     
  2. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Joined:
    Aug 9, 2009
    Occupation:
    Retired
    Location:
    Florida
    If it is a steam boiler there should be a gauge glass. You can install a tee in the lower tapping for the glass and install your probe in it.

    John
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. dsorkin

    dsorkin New Member

    Joined:
    Jun 2, 2010
    Location:
    New Jersey
    Thanks for the reply John. I had also thought of doing that but wasn't sure if it would be safe enough. Do you know if that is a recognized installation method or if there was ever an inspector in my house they would get a good laugh at my expense from it? I like this idea because besides not having to drill a hole in the boiler it would also allow me to easily change the height of the probe if I need to make adjustments.

    Thanks!

    Here are some pictures, note probe in lower right of photo.

    [​IMG]

    [​IMG]
     
    Last edited: Jun 3, 2010
  5. dsorkin

    dsorkin New Member

    Joined:
    Jun 2, 2010
    Location:
    New Jersey
    Follow up - I spoke with Hydrolevel (manufacturer of the LWCO) and they confirm the installation of the probe into the riser pipe.

    Many thanks!
     
Similar Threads: tapping steam
Forum Title Date
Boiler Forum Hoffman valve on 2 pipe steam? Dec 19, 2016
Boiler Forum Steam Boiler Control Mar 17, 2016
Boiler Forum Steam radiator valve question Jan 19, 2016
Boiler Forum Is it time for a new steam boiler? Jan 3, 2016
Boiler Forum From Steam to Water considering old pipes and higher pressure Oct 25, 2015

Share This Page