Discussion in 'Plumbing Forum, Professional & DIY Advice' started by essjay, Aug 21, 2013.

  1. essjay

    essjay New Member

    Joined:
    Nov 12, 2012
    Location:
    Pennsylvania
    I have a taco zone valve on a supply line. Can I safely cut the pipe after the zone valve and add in a ball valve if the taco valve has no power to it. In other words, can I assume the taco valve closes 100% as the norm (are these valves quality enough to assume this?) with no power applied.
     
  2. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Joined:
    Aug 9, 2009
    Occupation:
    Retired
    Location:
    South*East
    Simple answer NO. You will still have pressure from the return side.

    John
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. essjay

    essjay New Member

    Joined:
    Nov 12, 2012
    Location:
    Pennsylvania
    John,

    Thanks for the quick reply. Didnt think about the return side, but this line does a 90 with a drop of 7 ft, so I assume water loss will be minimal with this to equalize (didnt explain this though in original post).

    Any thoughts on the valve though?
     
  5. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    If you will not get water from the "return side" then you will not get any from the supply side either, regardless of whether it is open or closed because both sides will have equal pressure, the valve just stops flow. Normally, you would put the ball valve in front of the zone valve, but why are you doing it anyway?
     
  6. essjay

    essjay New Member

    Joined:
    Nov 12, 2012
    Location:
    Pennsylvania
    Follow up:

    There was no flow, as per hj. Lost about a cup of water from the line when cut, as expected. Ball valve inserted.

    Taco Zone valves, depending on type (I think I have the 571s) have the following specs, so had I read this I would have known:

    Taco Zone Valve 571-2 3/4" Features:

    Normal Flow Rate - 4 1/2 to 6 GPM
    Volts - 24V / Amps - 0.9
    Equalivent Feet of Pipe - 20
    Pump Head Feet of Water - 65
    Maximum Working Pressure - 125PSI
    Sweat Connections
     
Similar Threads: Taco Zone
Forum Title Date
Plumbing Forum, Professional & DIY Advice two zone circulator electrical connections taco to becket afg Nov 9, 2010
Plumbing Forum, Professional & DIY Advice Taco On Command hot water recirc pump installation gone kind of wrong... Jul 26, 2015
Plumbing Forum, Professional & DIY Advice Taco 705-2 variable speed injection pump with ECM energy efficient pump? Apr 17, 2015
Plumbing Forum, Professional & DIY Advice No hot water to shower, TACO circulater possible problem Apr 16, 2014
Plumbing Forum, Professional & DIY Advice taco circulator with different model number Feb 3, 2014

Share This Page