T&P Valve failure???

Discussion in 'Water Heater Forum, Tanks' started by dirtmover, Aug 6, 2009.

  1. dirtmover

    dirtmover New Member

    Joined:
    Feb 16, 2007
    Location:
    Ontario
    I shut my water heater down for two weeks while on vacation. I turned the heater back on this afternoon and after running for about an hour the T&P valve opened up discharging water over the basement floor. Is this a common failure mode for this type of valve after the heater has been allowed to cool down? I've replaced the valve and am watching closely as it heats up again.

    [​IMG]
    T&P Valve looking at two sides.
     
    Last edited by a moderator: Aug 18, 2009
  2. SteveW

    SteveW DIY Senior Member

    Joined:
    Feb 11, 2005
    Location:
    Omaha, NE
    Could be a bad T/P valve -

    or could be thermal expansion!

    Do you have a pressure reducing valve? If so, do you have an expansion tank?
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. dirtmover

    dirtmover New Member

    Joined:
    Feb 16, 2007
    Location:
    Ontario
    I am on a well so, assuming there is not a check valve in the tank(?), the pressure tank should act as an expansion vessel - correct? The pressure was not high according to the gauge and the temperature did not seem excessive.

    BTW, it seems fine now with the new valve. I'm just curious if it's common for them to fail after allowing the tank to cool and sit unused for a few days.
     
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    In normal operation, you don't start your WH with all cold water. Because you did, you ended up with a lot more expansion than you normally would. That unusual volume might have given you problems with your bladder tank if the static pressure in it is low. Try shutting off the pump, opening a valve until the water stops flowing, then check the pressure in your tank. It should be 1-2# less than the turn-on pressure.

    Or, your old valve could have worn out.
     
Similar Threads: Valve failure
Forum Title Date
Water Heater Forum, Tanks Water Heater drain valve failure Jun 26, 2014
Water Heater Forum, Tanks Water heater control valve? Bradford White MI40T6FBN Jun 26, 2015
Water Heater Forum, Tanks Connection to drain valve? May 12, 2015
Water Heater Forum, Tanks Water heater gas valve replacement costs Mar 13, 2015
Water Heater Forum, Tanks Water heater relief valve drainage Mar 10, 2015

Share This Page