T&P Valve failure???

Discussion in 'Water Heater Forum, Tanks' started by dirtmover, Aug 6, 2009.

  1. dirtmover

    dirtmover New Member

    Messages:
    64
    Location:
    Ontario
    I shut my water heater down for two weeks while on vacation. I turned the heater back on this afternoon and after running for about an hour the T&P valve opened up discharging water over the basement floor. Is this a common failure mode for this type of valve after the heater has been allowed to cool down? I've replaced the valve and am watching closely as it heats up again.

    [​IMG]
    T&P Valve looking at two sides.
    Last edited by a moderator: Aug 18, 2009
  2. SteveW

    SteveW DIY Senior Member

    Messages:
    1,055
    Location:
    Omaha, NE
    Could be a bad T/P valve -

    or could be thermal expansion!

    Do you have a pressure reducing valve? If so, do you have an expansion tank?
  3. dirtmover

    dirtmover New Member

    Messages:
    64
    Location:
    Ontario
    I am on a well so, assuming there is not a check valve in the tank(?), the pressure tank should act as an expansion vessel - correct? The pressure was not high according to the gauge and the temperature did not seem excessive.

    BTW, it seems fine now with the new valve. I'm just curious if it's common for them to fail after allowing the tank to cool and sit unused for a few days.
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,357
    Location:
    New England
    In normal operation, you don't start your WH with all cold water. Because you did, you ended up with a lot more expansion than you normally would. That unusual volume might have given you problems with your bladder tank if the static pressure in it is low. Try shutting off the pump, opening a valve until the water stops flowing, then check the pressure in your tank. It should be 1-2# less than the turn-on pressure.

    Or, your old valve could have worn out.
Similar Threads: Valve failure
Forum Title Date
Water Heater Forum, Tanks Water Heater drain valve failure Jun 26, 2014
Water Heater Forum, Tanks Mixing valve for water heater with recirculating line. Dec 20, 2014
Water Heater Forum, Tanks Air causing problems with bypass/mixing valves? Sep 17, 2014
Water Heater Forum, Tanks Bradford White RTV-75 Drain Valve Sep 13, 2014
Water Heater Forum, Tanks Water heater size with and without tempering valve Jul 12, 2014

Share This Page