    Purchased a house last year in October. House has a well for irrigation. Not knowing anything about the well or last time it was used, I assumed all components (pump, pressure switch and tank tee, and pressure tank) were shot and needed to be replaced to be operational. I've removed the tank and associated plumbing adjacent to the 6" casing located in an 8 foot deep concrete pit. I decided to pull the pump, not knowing how deep it actually went.

    Pulling pump was relatively easy. Ended up being about 150 feet deep, a Myers 1/2hp, 230V 4" submersible pump (looks about 20 years old) with 1" poly tubing. Over the next couple of weeks I put new electrical in the pit and reconnected the pump to see if it was operational. Ended up running, so I decided to throw it back down the casing, and viola, I got a decent about of water. I purchased a new pressure tank (Amtrol of course because I live right near their manufacturing site) and tank tee. Installed all components and let her rip.

    Here's my problem: Pump runs constantly. Pressure in the tank tee never rises above 25psi. Pressure tank precharge is set at 38psi with a 40/60 pressure switch. I don't believe water is filling up pressure tank, which makes sense if well pump cannot overcome the precharge in storage tank. Please confirm that the general consensus is that my pump's performance is weak and the remedy to the solution is to purchase a new pump. I understand that there could be a leak that is allowing water to discharge into the casing, but I think this is highly unlikely. Let me know what you think.
  2. valveman

    valveman Moderator Staff Member

    Messages:
    4,472
    Location:
    Lubbock, Texas
    Make sure your gauge is good. I am showing a 12 GPM, 1/2HP Myers will produce 38 PSI even if the water level is at 150'. But for that pump to be able to build to 60 PSI the water in the well will have to be less than 100' deep.
  3. joshpjost

    joshpjost New Member

    Messages:
    4
    Location:
    Massachusetts
    The Myers 1/2hp pump is a 5GPM unit.
  4. Reach4

    Reach4 Active Member

    Messages:
    2,296
    Location:
    IL
    I think you are implying that no water is being used when you are watching the pressure. If you have not done so, close the valve that is after the pressure switch and tank to be sure there is not some irrigation pipe accepting water.
  5. joshpjost

    joshpjost New Member

    Messages:
    4
    Location:
    Massachusetts
    Reach4, correct. I have shut off the valve after the pressure switch to the hose bib pipe. There are no other pipes other than the intake from the pump.
  6. Reach4

    Reach4 Active Member

    Messages:
    2,296
    Location:
    IL
    Then I think you have thought of all of the alternatives, and your conclusion is correct.
  7. joshpjost

    joshpjost New Member

    Messages:
    4
    Location:
    Massachusetts
    Would a new 5GPM 1/2HP pump be capable of reaching >60psi at 150ft deep? How does one determine this? Using standard 1" poly pipe
  8. Reach4

    Reach4 Active Member

    Messages:
    2,296
    Location:
    IL
    Use pump curves or tables. Note that 60 PSI is about 140 feet of head. So if you want to be able to pump from 150 feet, make sure that 290 feet is on the curve.

    http://www.pumpsandwells.com/mm5/PDFs/B5-25GS.pdf is a nice manual for Goulds. It has not only graphs, but tables where the compensation has been taken care of. Other makers have similar manuals and similar pump capacities.

    Note that your pump should take a minute or more to fill the pressure tank to avoid short cycling.
  9. LLigetfa

    LLigetfa DIYer, not in the trades

    Messages:
    4,001
    Location:
    NW Ontario, Canada
    I think you need to test out that hypothesis. Assuming no other checkvalve than what is in the pump, a simple pressure test would confirm it.
Similar Threads: Submersible Pump
Forum Title Date
Pumps and Tanks Well Forum & Blog Submersible pump pulled, minimal flow in test bucket.... Sep 3, 2014
Pumps and Tanks Well Forum & Blog Submersible pump well problem Aug 1, 2014
Pumps and Tanks Well Forum & Blog Protecting a submersible pump using flowmeter Jul 26, 2014
Pumps and Tanks Well Forum & Blog Tankless Submersible Well Pump losing pressure Jul 7, 2014
Pumps and Tanks Well Forum & Blog Submersible Pump Problem Jun 30, 2014

Share This Page