    Ok all at the end of last years heating season my pressuretrol took a dive and would only work if i banged on it or played with the adjustment. I found a brand new one at my local supply house and replaced it tested it and all seemed good. Before the system was fired this year I drained the system before this heating season refilled with fresh water(halfway up the sight glass...had to release pressure from under the pressuretrol and all seemed ok...in the last week or two i have had to play with the pressure adjustment to keep the furnace fired long enough to heat my second floor...

    Heres the layout...18x40 brick construction attached on both sides...
    first floor one 5 foot radiator under them living room window in the same room as the only therm in the house.
    second floor 4 rooms each with various sized radiators.
    not sure of the valving on each unit...

    Question is what would cause me to have to fuddle with the pressuretrol...again...should i unscrew it from the pigtail and see if it is pressurized there...if so waht is causing the undue pressure.

    Thanks
    Racer
  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Is the pig tail clear and not full of rust and crap?
  3. racerc20

    racerc20 New Member

    Messages:
    6
    Location:
    NY
    dont know ill check later.
  4. racerc20

    racerc20 New Member

    Messages:
    6
    Location:
    NY
    OK went down and cleared a bunch of rusty brown black water from the upper drain after the low water cutoff...then i removed the pig tail has a union on it so was easy to get out...clogged solid to the pressuretrol...i took a piece of 12ga coppe wire and ran it through the pig tail as far as i could get from both sides..got air and water to flow through it...lowered the cut in back down and am testing the unit now...it fired right up and the pipes are alread creaking to life...

    If this works peter i owe you and stewie a cold one...the pig tails are usually a preset length correct. i should be able to just pick up a new one right?

    Thanks...
    Racer
Similar Threads: Steam heat
Forum Title Date
HVAC Heating & Cooling vacuum vs non-vacuum valves in a 1 pipe low pressure steam heating system ? Jan 16, 2012
HVAC Heating & Cooling (uk heating) steam from elson tank Nov 22, 2008
HVAC Heating & Cooling Old Oil Fired Steam Boiler with Side Arm Water Heater Jul 9, 2008
HVAC Heating & Cooling Convert steam radiators from oil to gas May 7, 2013
HVAC Heating & Cooling honeywell true steam vs april air 800 steam humidifier, vs ewc ultrazone May 19, 2012

Share This Page