Hi,
I know that typically there is a 1.33 factor figured in for piping. What would be a good factor in the case where the new boiler is serving a third floor apartment? Compared to an apartment on the first floor, there are 7, 1 or 1-1/4 ~20' each, pipes (~ 140 more feet) running through the walls of other apartments to supply the 8 third floor radiators.

One pipe steam, EDR = 261, radiator load 62,500 BtuH

Thanks
 
Last edited:

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
You also need to know the input of the radiators, however, steam is a different animal than forced hot water. When the system was originally sized and installed the boiler was chosen to match the radiation and while I'm sure the heat loss of the home has been improved over the years through the addition of better windows, doors and insulation, the radiation and piping still need to be properly fed so to speak so when installing a new steam boiler, the best practice is to closely match the output of the existing unit because a smaller boiler will make steam faster but with less volume and what happens is the piping and radiators take the steam and the boiler water level drops either shutting off the burner ( short cycling) or if you have an automatic water feed, it feeds more water and on the off cycle e boiler over fills when the condensate all comes back.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks