SPA Disconnect Feeder Ground

Discussion in 'Electrical Forum discussion & Blog' started by smahon, Jul 24, 2009.

  1. smahon

    smahon New Member

    Messages:
    2
    I've read, searched and scratched and still wonder. I will be wiring an outdoor, 4-wire, 50A SPA this weekend. I have the permit and need to know:

    1) Can the EMC conduit (to be installed "on" my house) from my Service Panel to my Spa Disconnect (50A GFCI contained in disconnect panel) act as my ground to the Spa Disconnect? Planning to run 3 - #6 THHN, black, red, white for load and neutral to the disconnect. If not, I presume I will need to add a #10 THHN green for ground.

    2) What is the appropriate method (tubing/wire type) to wire the supply side of the disconnect into the side of the tub and around to the other side for connection to the equipment panel?
    Last edited: Jul 24, 2009
  2. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Messages:
    1,001
    Location:
    NY State, USA
    1) Absolutely not. The ground for a spa circuit when run outside MUST be insulated.
    Yes, #10 would normally be sufficient, but the installations instructions may call for larger.

    2) I assume you mean from the load side of the disconnect.
    This depends on the spa itself. You can use up to 6' of liquidtite flexible conduit.
  3. smahon

    smahon New Member

    Messages:
    2
    Thanks, that's what I originally understood too, until I read somewhere in another part of the general code, that EMC would suffice as a ground for a feeder circuit. Anyhow, I ended up buying grey schedule 40 uv rated PVC, so the question is moot. Also, the electric supply would only sell 500 feet rolls of #10, so I bought #8 green for the ground (they would cut 8 or larger).

    Now, for the load side. Does that 6' of liquidtite only apply to the exposed portion? I have to run wire into one corner of the spa and around two sides to get to the connection panel, about 12' inside. I was planning on running PVC up to the spa, then connect it to liquidtite for the run through the access hole (that I need to drill) to the connection panel. It would be much easier if I can run 6' of liquidtite outside the spa in addition to the 12' inside. For that matter, does the run inside the spa even need to be in liquidtite?
    Last edited: Jul 24, 2009
Similar Threads: Disconnect Feeder
Forum Title Date
Electrical Forum discussion & Blog Distance From Meter to Disconnect Jun 26, 2014
Electrical Forum discussion & Blog Heat pump service disconnect Jan 28, 2013
Electrical Forum discussion & Blog Building Service Disconnect question Jan 21, 2012
Electrical Forum discussion & Blog how do i disconnect power on a split buss? Jan 5, 2012
Electrical Forum discussion & Blog Proper treatment of disconnected circuit Jan 2, 2012

Share This Page